    Husky ice machine



    Hi I have been having problems with a husky ice machine (no details wotsoeva) on it I would say maybe 60kg it's a decent size-:
    Problem started about 6 weeks ago were customer said there was a big block of ice on evap plate and no cubes was dropping,so with customer been a good 40min drive I said turn machine off leave over night switch back on in morning and go from there,anyway machine worked fine again for 4-6 weeks please any advise or suggestions would be great

    Picked machine up and ran in workshop first thing I noticed was compressor was freezing up like sweating it was that cold so took gas out and recharged 400g r134a
    Left on test same thing comp started icing up
    What I did notice is the discharge is nice and warm for maybe first 3-5 mins of a cycle then rapidly starts to loose heat which is obviously no good when it goes to defrost the plate,hot gas valve working all ok any suggestions
    Comp is danfoss sc21g r134a LBP



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Husky ice machine

    Sounds like liquid coming back, confirm with a superheat reading. might be an issue with the cooling coil coming away from the cubes.

    alec
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Husky ice machine

    have you changed the drier? 134 tends to block it.
    Is the evaporator surface freezes evenly?

  4. #4
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    79
    Posts
    195
    Rep Power
    17

    Re: Husky ice machine

    Please don't take this as professional advice, I'm not a refrigeration guy. I had an old ice making machine give intermittant freezing back to the compressor and very slow ice making. I had to call an expert eventually who found the expansion valve had been replaced with the incorrect type previously. He installed a new valve which he said was 'unmopped' and it did the trick. He did explain at the time what the unmopped part means but it was more than a few years ago and unfortunately I can't remember.