Results 1 to 4 of 4
  1. #1
    Join Date
    Dec 2009
    Location
    Sweden
    Age
    48
    Posts
    15
    Rep Power
    0

    Cool Carrier 30RA turning stopping at night



    Hi!

    I have a Carrier 30RA 017. It uses a Pro-dialog Plus Control and operates in local on mode. Problem is that it stops sometimes during the night or at the weekend and when i come, there are no alarms but the unit is in local off mode. I turn it on to local on and it starts and works ok. It has worked for the last 3 weeks before it stopped this time.

    Alarm history shows 9, 37, 46, 36, 30. I also noticed that the alarm lights appear to be blinking in some sort of sequence even when the unit is running.

    any ideas?



  2. #2
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Carrier 30RA turning stopping at night

    Could you give me the complete model of the machine? codes you mention do not appear in the manual.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Carrier 30RA turning stopping at night

    Most of those codes seem to indicate either sensors or external switches/faults causing a shut down.

    Pro-Dialog Manual...
    http://eto.carrier.com/litterature/cm/13048.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Carrier 30RA turning stopping at night

    Hello Brian Have the same problem with the same machine. Our machine usually stays in Remote. when the power goes out it reverts back to local off. hope it helps.