    running pressures



    Hi guys,i'm new to the forum so bear with me.
    Done a leak pressure test today to a searle beer chiller system.The system had been left to run with very little gas in it so i suspect the compressor to have damage as it was hot and noisy.Found 2 leaks which i repaired,vac'd out the system and recharged with r407c.Once powered up the compressor became noisy again and the running pressues were near identical,60psi suction and 50-60 discharge.Iv'e never came across this before so any advice on whats going on would be appreciated.I personally think the compressor was only moving the refrigerant around the system as the discharge line had no heat to it at all+no dicharge pressure?!



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: running pressures

    If the compressor is wired correctly and not running backwards then the equalised pressures indicate that the compressor is what we call ' a non pumper' and needs replacing.

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: running pressures

    '' a non pumper ''

    thats the politest description of f**ked I've ever heard

    R's chillerman
    If the World did not Suck, We would all fall off !

  4. #4
    Join Date
    Jul 2006
    Location
    norfolk
    Age
    51
    Posts
    737
    Rep Power
    24

    Re: running pressures

    we call it fooked
    check out my website www.airkooldomestics.co.uk

  5. #5
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: running pressures

    Check that the system has an expansion device in circuit!

  6. #6
    Join Date
    Jan 2013
    Location
    scotland
    Age
    44
    Posts
    52
    Rep Power
    12

    Re: running pressures

    Quote Originally Posted by flyinkiwi View Post
    Check that the system has an expansion device in circuit!
    The evaporator has an expansion valve but as far as im aware it was all ok just running short of gas.Surely the discharge temp straight from the compressor should be around 250-300psi.Sounds like a 'non pumper',never came across one before,any compressor ive seen that isnt working is usually seized or shorted out.
    Another thing we were debating over was on the condenser it stated r404a/r407c as the gas type,does this mean it would run with either or?In my experience r404a is for systems that run at a lower temperature ie chiller room,freezers etc.This beer cellar was set at 10 degrees centigrade.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: running pressures

    one example of a ''non pumper''

    http://www.refrigeration-engineer.co...achmentid=8091

    conrod snapped and punched through piston

    R's chillerman
    If the World did not Suck, We would all fall off !

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: running pressures

    if its a 3 phase scroll compressor then reverse a phase as the dont do much when running the wrong way

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: running pressures

    Check the tev to see what type refrigerant the system runs, R404A would work in a chiller application also.