Results 1 to 6 of 6
Thread: BTU/H to KWH Conversion
-
25-10-2012, 12:52 PM #1
BTU/H to KWH Conversion
Does anyone know of a good calculation for BTUH to KWH? I have found some calcs that say .29 KWH per MBTU. NOt sure how accurate this is. A good calc will help me figure enrgy savings when I am asking for funding for projects.
-
25-10-2012, 02:28 PM #2
Re: BTU/H to KWH Conversion
Hi
this is from ashrae handbook : Btu/h x 0.2930711 = W/hLast edited by Teuria; 25-10-2012 at 02:30 PM.
-
25-10-2012, 04:26 PM #3
Re: BTU/H to KWH Conversion
Coorsman777, just a very important correction:
1) Btu.h?!? It doesn't exists. Btu/h exists and is the rate of energy per unit of time » power.
2) Btu is already energy doesn't need be multiplied by h (time)
3) kW.h is energy. kW is power. kW/h doesn't exists...doesn't make sense
Teuria the correct answer is Btu/h x 0.2930711 = W.
Many people do this error...To make progress is never good enough, I want to do better and better and better
-
25-10-2012, 05:38 PM #4
-
25-10-2012, 05:47 PM #5
Re: BTU/H to KWH Conversion
No problem!
To make progress is never good enough, I want to do better and better and better
-
23-12-2012, 10:10 PM #6
Re: BTU/H to KWH Conversion
Dear Friend,
I think it would be better to check also http://www.engineeringtoolbox.com Also.
this site is one of the best online free conversion toolbox.
Regards