    Bitzer screw compressor type HSK 7451-80-40P
    Hi / Dears
    I have 2 Bitzer comp. one HSK & HSN the first -10 C : +40 C and other -35 C : 40 C . they have ECO connection . My question can i use the comp. type HSK in -35 C : 40 C too ?
    Thanks friends
    Feb 2012
    Bolivia
    270
    14
    Re: Bitzer screw compressor type HSK 7451-80-40P
    No!
    Depending on the type of refrigerant used, from -10 to -20°C the compressor motor will not cool enough with the refrigerant, motor protector will trip.
    Mar 2007
    Egypt
    55
    54
    Quote Originally Posted by aramis View Post
    No!
    Thank you for your reply could you please tell me about the min. evaporating temp. and can i use it in NH3 refrigerant?
    38
    definitly not ammonia as they are semi hermetics,
    Feb 2012
    Bolivia
    270
    14
    You can get all the answers you want from the manufacturer's site www.bitzer.de.
    All manufacturers specify a minimum evaporating temperature for their compressors depending on the refrigerant and design (model).
    You cannot use Bitzer semihermetic screws with R717 only the open type (OSK), are suitable.
    mond13's Avatar
    mond13 Guest
    as suggested above already the bitzer website offers an design tool with propper calculations. (also available as software to be downloaded)
    Dec 2006
    Iran
    43
    55
    I think also the coolpack software could help you on system analysis .