14-09-2012, 03:04 PM #401
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys i have a question when i can say my quench valve is defective this is a carrier microlink2
-
18-09-2012, 08:58 PM #402
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hai,hope that u can help me on this.
i have got a 69 -nt carrier transicold container on which i have changed exp valve (hermatic type) 2 times,but still the container running on a vaccum suction pressure.what would be the problem.
-
19-09-2012, 10:54 AM #403
Techs you've now decided to run compressors with cylinder head cover open. That's nice.
-
20-09-2012, 07:37 AM #404
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi there Kaushi, what temp are you trying to run the container at. With a frozen setpoint ( say -20.00deg C) R134A will run in a slight vacuum.
Have you changed the filter drier?, also what is the model number (69NT.............-...)as some boxes have a suction modulation valve and the newer ones have a stepper motor
really need more details
-
20-09-2012, 11:23 AM #405
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
reefermechanic
Last edited by reefermechanic; 30-01-2013 at 08:35 AM.
-
20-09-2012, 01:20 PM #406
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi reefermechanic
thanks for your anser ,plz send me ( smartsponge) to my email
troytroy@live.fr
terminal
-
20-09-2012, 06:11 PM #407
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
this model has a stepper valve. i am running this container at -20 st pt. the problem is container pulls down to a temp around -9to -11 and not below.stepper valve shows 100% opening.i have replaced the compressor for this unit because the old one had a piston damage and the whole unit was contaminated.i also flushed the system with R-11 before installing the new compressor.
-
20-09-2012, 06:14 PM #408
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
set point is -20 deg C.i have changed the filter drier. the unit has a stepper valve which shows a 100%opening on running the unit.
-
21-09-2012, 12:17 AM #409
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi there Kaushi, have you put the box thru a P6 test and listened for the stepper valve to open and close. Put a service manifold onto the box and check the suction pressure during the test. You will be able to see if the valve is opening or closing correctly. I have had a container that has had a jammed stepper valve piston and also have had a valve on another box with the valve piston removed. The box with the piston missing was because some one didnt have a spare valve head and it was motoring closed and staying there.
The P6 test will show if the box is metering or not, does the box have a recip compressor or a scroll as the setups are very different. The scroll has extra valves in the system e.g LIV, LSV, ORV, USV
We really need to know the model number (it will be something like 69NT40-541-001)
-
23-09-2012, 03:18 AM #410
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
kaushi try to check the stepper motor if the stepper have a good resistance follow the steps
1st disconnect the connection of stepper motor going to power pack
2nd get the resistance of (a-b) or red and green wires
3rd get the resistance of (c-d) or white and black wires
the good resistance if im not mistaken 72ohms
hope you solve this
-
23-09-2012, 03:19 AM #411
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
and kaushi try to check if the software of controller is match up to the unit
-
25-09-2012, 12:51 PM #412
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HELLO ALLS,
please help me about PrimeLine 561-018 model. during start Auto2 PTI, RM (remote monotoring) doesn`t start counting, it's stay on number 180, causes Auto2 PTI cannot not be started.
already configurated and software back.
any suggestion.
-
28-09-2012, 01:18 PM #413
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi reefer contr,
pls check your e-mail.
see you
reefer mecahnic
-
28-09-2012, 01:23 PM #414
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi Kaushi,
your problem solved??
see you
reefer mechanic
-
28-09-2012, 03:11 PM #415
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hey reefer mechanic. I have 2 mitsubishi CPE52-3BAA that I have to repair. Do you have a parts manual and maintenance manual??
-
28-09-2012, 03:49 PM #416
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi HveecAC
check your e-mail.
see you
reefer mechanic
-
29-09-2012, 04:03 AM #417
-
29-09-2012, 06:33 PM #418
-
05-10-2012, 08:42 PM #419
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Every One here..
I am New to this website. But I Highly appreciate contribution of Mr. Reefer Mechanic to this Forum and website.
Best Wishes for you Reefermechanic !
Regards,
Dave
-
05-10-2012, 08:46 PM #420
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Every One here..
I am New to this website. But I Highly appreciate contribution of Mr. Reefer Mechanic to this Forum and website.
Best Wishes for you Reefermechanic !!
Regards,
Dave
-
06-10-2012, 07:35 AM #421
-
06-10-2012, 11:04 AM #422
-
06-10-2012, 05:10 PM #423
-
06-10-2012, 07:10 PM #424
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
thanks guys, first of all soory for the delayed reply.it was actually a jammed stepper valve piston.i replaced it and now the container is fine.
-
11-10-2012, 10:12 AM #425
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hey Reefer Mechanic! I'm back again. I was wondering if you could email me the Daikin TR02-14 operation manual. I don't have it and I have gotten in 2 Daikins to repair. Thanks for your help.
-
11-10-2012, 12:39 PM #426
-
15-10-2012, 11:42 PM #427
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey there guys, can anyone tell me what type of oil separator is on a NT20-531-301, I have been told it is a float type. the reason I am asking this is that it seems to be jammed open and putting hot discharge gas back into the sump of the scroll comp. Can anyone tell me how the oil return solenoid is cycled or is it powered all the time? When I disconnect the oil return valve for testing the system running pressures come back to within the normal range and the box cools.
The box has been running ok and now is struggling at -20. It failed the P10-2 test. after disconnecting the oil return valve solenoid coil I ran the test again and it passed. It isnt desirable to leave the oil return valve disconnected. also the condenser fan motor is on all the time and the discharge pressure gets as low as 650Kpa, I thought the condenser fan motor cycled or is that only in perishable mode(above 0 deg) the suction pressure seems to be ok for a while then goes rather erratic. The refrigerant level is way up in the top sightglass in the receiver which I think is not normal and stays there.
I am looking at the TX valve at the moment and possibly the oil separator as well,
Any help would be very much appreciated
regards
-
16-10-2012, 06:17 PM #428
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Phil Landon,
May be I can help you for this, “Can anyone tell me how the oil return solenoid is cycled or is it powered all the time?”
The oil return solenoid valve in this model is normally open which allow oil to return during off cycle. Hence when the cycle is ON, ORV is normally closed by constant power supply.
Regards,
Dave
-
03-11-2012, 03:00 AM #429
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HELLO ALLS, did anybody have manual for thermoking crr40 (super reefer type) .
i always facing problem of poor body insulation due to high ambient temp in here.
-
13-11-2012, 05:28 PM #430
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello everyone
I have a problem with carrier thinline compressor overhjeating. I changed compressor, but same thing again. compressor run for some time, and then stops with AL24. Anyone can help?
Thanks
-
14-11-2012, 07:46 AM #431
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
................................
Last edited by reefermechanic; 27-02-2013 at 09:15 AM.
-
18-11-2012, 07:05 AM #432
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Last edited by carrier_trained; 18-11-2012 at 07:07 AM. Reason: update
You cant polish a turd!
-
30-11-2012, 11:13 PM #433
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello reefer mechanic,
i am having prob wid stracool reefer.....st pt is -20 ret is -14.5 sup is -13.4 suc pre is -1.0 bar dis pre is 3.2 bar....***** level is ok.....check evap fans ok.....condensor is ok...........perform function test on one by one component shows error on Evap XV.......try to replace it...but bcoz of ice and rust its very hard to take out...dnt know wot to do? plz help me
-
10-12-2012, 07:56 PM #434
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey guys,
i am having 2 carrier thinline 69-nt-511-363 conts that is showing problems
1:-first one enters into defrost,but after comming out does not start automatically,one has to go there restart the unit.
2:-the container is not entering into manual defrost.
both these containers have an active al54 alarms.one of them i changed the sensor(supply)and put p5 but still alarm active.NEEDS HELP URGENTLY
-
10-12-2012, 08:23 PM #435
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
...............................................
Last edited by reefermechanic; 18-12-2012 at 04:38 PM.
-
11-12-2012, 07:00 AM #436
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi kaushi,
your problem solved?
reefermechanic
-
29-01-2013, 02:42 PM #437
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi guys. I m here now."reefer container turkey" in Facebook..see youreefer mechanic
-
03-02-2013, 02:16 PM #438
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
...........................................................
Last edited by Brijeshdave; 05-02-2013 at 02:12 PM.
-
04-02-2013, 01:30 PM #439
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Awaiting your reply. Sir,
Regards,
Dave
-
05-02-2013, 01:19 PM #440
-
06-02-2013, 05:10 PM #441
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello reefermechanic
I'm an reefer electrician but new to this job. I have a problem on a carrier reefer, model 69nt40-541-015 wich has a ML3 controller. In proximately one month it fried 2 controllers. I had the container not working at all, replaced the controller, it worked fine, did the PTI, went on a trip and when it returned it was just like the removed controller. sometimes it works but giving alarms, other times the display and reefer are completely dead. It has 2 pins on connector KA (KA9 and KA10) that are the power supply to the controller, ( 33V betwen them) I think. Does the controller have any other power supply? and if not do you think that the transformer can have some sort of problem? by the way do you know the language of programming used in these controllers? is it ladder or FBD or is it something mor complex like C++?
-
06-02-2013, 10:25 PM #442
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Friend
I will help you. Pls contact me via reefermechanic@yahoo.com.
See you
reefermechanic
-
13-02-2013, 11:29 PM #443
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Guys, I'm looking for a service manual for a MHI CPE52-* with a MMCC111 controller.
I have looked on the internet and have started looking through this forum. I am at work at the moment and can't spend all day looking for this. If someone could give me a heads up it would be greatly appreciated.
Thanks
Dean
-
19-02-2013, 11:15 PM #444
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi again,
I found some time to scan through all the pages today and I think I found what I was looking for.
Thanks
Dean
-
26-02-2013, 05:20 PM #445
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello sir how are you, my name is jayin ihave some some douts can you help me?
-
26-02-2013, 05:22 PM #446
-
26-02-2013, 05:25 PM #447
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
sorry i ask to reefer mechanic
-
26-02-2013, 06:09 PM #448
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
reefer mechanic please give your e mail id 'reefermechanic@yahoo.com' this id is not working
-
26-02-2013, 07:02 PM #449
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
dear jayink87
how can i help you?
i m online now for reefermechanic@yahoo.com
see you
reefermechanic
-
17-04-2013, 08:53 PM #450
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello there! I have a Thermo King with Magnum-924 reefer unit. When it running for couple hours, the compressor totally frozen up. The ***** level is ok(not overcharged), fan works. Any help with this issue will be really appreciated. Thanks. Yury. There is my e-mail:gove777@hotmail.com
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM