Results 1 to 4 of 4
-
01-09-2012, 12:43 PM #1
Help fitting Hitachi Horizontal Scroll ZS7516S1
IMG_20120901_121904.jpg
Hello
I am fitting a Hitachi horizontal scroll Model ZS7516S1 (see picture).
It's replacing an obsolete Rivacold compressor for a Pastofrigor Multideck.
Have I got this right (please see picture):
The accumulator fits directly onto the suction with no inclination the the left or right - this causes me a problem because I don't think there's enough room under the unit for it.
Is the high pressure connection on the bottom of the compressor for the capillary tube, presumably for the HP switch and cannot be used for the main discharge?
All comments welcome.
Thanks.
-
01-09-2012, 03:08 PM #2
Re: Help fitting Hitachi Horizontal Scroll ZS7516S1
found this
http://www.mediafire.com/view/?a9rvulbi54etur9
and this
http://www.mediafire.com/view/?4u9m2dofmijls24
capillary line is for liq injectionLast edited by install monkey; 01-09-2012 at 03:23 PM.
-
01-09-2012, 04:09 PM #3
Re: Help fitting Hitachi Horizontal Scroll ZS7516S1
That'll be the discharge on the bottom then! And the liquid injection will be an option !
Thanks!
-
03-09-2012, 09:18 PM #4
Re: Help fitting Hitachi Horizontal Scroll ZS7516S1
Can anyone tell me if the accumulator is correctly positioned on this compressor, or does it need to be completely vertical elsewhere in the suction line?
(I know the liquid injection capillary is sticking out the discharge pipe)