Results 1 to 6 of 6
Thread: Sanyo p29 fault
-
11-07-2012, 05:55 PM #1
Sanyo p29 fault
Hi all one of my friends has a Sanyo ac system which is displaying p29 fault any idea what the fault is and what parts are req to fix thiis
-
11-07-2012, 08:10 PM #2
Re: Sanyo p29 fault
P29 is a compressor fault or DCCT failure ,It basically telling you the inverter compressor failed to start.
Model numbers make this a whole lot easier....
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
22-07-2012, 04:13 PM #3
-
22-07-2012, 04:27 PM #4
-
27-07-2012, 04:02 PM #5
-
04-08-2012, 10:21 AM #6
Re: Sanyo p29 fault
You need to check the HIC board and also to measure the windings of the inverter (hope you have some ohms on each windings). If its broken you can stll run the machine until you replace it using the dipswitch on MB.
Cheers