chilled water pump power tripping
Hi All,
Recently i changed bearing for the pump, when i try to switch it on the power trips. kindly let me know what could cause the problem
-
17-05-2012, 02:42 PM #2
Re: chilled water pump power tripping
Check the resistance of the between the 3 windings of the motor, it should be the same. if not, you need to rewire or replace the motor.
-
17-05-2012, 04:53 PM #3
Re: chilled water pump power tripping
As chemi-cool states check motor windings but also check that motor and cables are clear to earth and that following the re-bearing job the pump still runs free with no tight spots.
It may be an idea to check that your incoming phases are intact and that the contactor and overload sets are operational.
-
18-05-2012, 03:18 PM #4
Re: chilled water pump power tripping
Hi
i would make sure the rotor and immpeler are free, and not locked ,before doing anything else !!
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
21-05-2012, 10:21 AM #5
Re: chilled water pump power tripping
Does this pump run on a vsd?
-
30-06-2012, 10:06 AM #6
Re: chilled water pump power tripping
is it direct coupled? does it spin by hand?
-
21-07-2012, 07:07 PM #7
Re: chilled water pump power tripping
hy. try to change conexion from star to delta. have to work.
-
22-07-2012, 10:56 PM #8
Re: chilled water pump power tripping
Is it a thermal protection or the fuse is tripping ? If it is a thermal protection is well calibrated ? What kind of pump is it ? Star delta ? Direct start ? More data please !