Results 1 to 13 of 13
  1. #1
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    trane ssm controllers
    Does anyone know how to reset the hours run on the ssm controllers and do you need a password.
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    Re: trane ssm controllers
    Quote Originally Posted by redroge View Post
    Hi redroge.
    I am sure I have it somewhere, can you remember what model chiller it is for?
    Grizzly
  3. #3
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14
    Hi,
    As far as I know there is no SSM controller.
    There is SMM and SCM.
    In SMM you cannot reset hours and starts.
    In SCM you cannot reset hours and starts as standard procedure but you can remove the EPROM and put it again. Then you may have HRD4 alarm and reset hours and starts of ALL compressors but you also have to reprogram the module.
    CV
  4. #4
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    my mistake its smm on a cgah225 chiller and its coming up with service demand on the screen
    saw a van in the states with Grizzly refrigeration on the side! has someone gone multinational.
  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    I wish!
    Oviously they make do with the bear minimum!
    Hopefully what I have sent you will help.
    Grizzly
  6. #6
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    Hi grizzly
    not recieved anything what info have you got
    cheers redroge
  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    Hi grizzly
    cheers redroge
    Now you have it!
    What do you think?
    Will it help?
    Grizzly
  8. #8
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19
    well did it help??
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
  9. #9
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    Been back today that info dos,nt seem to relate to smm controllers !
    Phoned trane to ask what service demand means and they refuse to give any information,anyway the customer is,nt having any more trane chillers as there aftersales is so bad.
  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    I beg to differ what I gave you should work.
    Refer to F4, also refer to password lock out F501.
    Maybe I did not give you enough.
    refer to the attached.
    Grizzly
  11. #11
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    Thanks grizzly
    Could,nt get past Fp will have another go next week when back at work (on a three day week).
  12. #12
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19
    Thanks grizzly
    been back to site today all sorted.
  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    Thanks grizzly
    Glad to be of assistance.
    Grizzly
Posting Permissions