    Looking for hot gas flow control valve
    Hello guys, as per title, I'm looking for a hot gas diverting valve, with analogue regulation, able to divert hot gas into a reheating coil.
    Refrigerant R410A (PS45 bar), capacities from 10 to 100kW.
    Anyone can point me to any manufacturer or tech sheet?
    Aug 2009
    New Zealand
    2,554
    Re: Looking for hot gas flow control valve
    Hi NNN,
    could you use a large EEV for this application!
    Mar 2006
    Merate (LC) - Italy
    2,549
    Maybe, but the existing EEV drivers need an evaporating pressure transducer and temperature probe, which have no meaning here.I would like a solution for a series production.
    3,853
    38
    Hi NNN,
    have you looked a Danfoss PMFL. you can get close regulation with them.
    Aug 2009
    New Zealand
    2,554
    I am sure, that some where in the Carel documentation, does show hot gas application.
    You just need to configure a bit of hardware and software to drive the valve. (if not standard)
    Convert your 4-20mA or 0-10V to what ever the valve requires , (presumed that PID is already sorted)
    Mar 2006
    Merate (LC) - Italy
    2,549
    Thanks everybody. I'll have a look at your hints.
    Mar 2006
    Merate (LC) - Italy
    2,549
    It definitely does, but as a back pressure regulation. Anyway it's a place to start.
    Aug 2009
    New Zealand
    2,554
    I should read the whole tread first!
    have a look at this company
    http://www.buerkert.com/
    Mar 2006
    Merate (LC) - Italy
    2,549
    mmmmh... no.
    Aug 2009
    New Zealand
    2,554
    Not a standard product,
    They did in the past, sort of state that if you had a process fluid (liquid/vapour/gas) that needed controlling they could control it.
    Email them to find out.
    If I am wrong, then I am wrong, if I am right then you win.
    Aug 2007
    Seattle, WA. USA
    56
    27
    Not sure if this is what you are looking for but it might be worth a read.
    http://www.parker.com/literature/Lit.../rs/25-95D.PDF
    Mar 2006
    Merate (LC) - Italy
    2,549
    Yes, but that's ON/OFF. I was looking for a modulating valve.
    Thanks anyway.
    May 2006
    India
    399
    Check with sporlan .........