    Hi Guys,
    Can some explain (In simple terms) the benifits betweer internal and external equallised expansion valves.
    I have on a few occasions, to get myself out of trouble fitted an internal valve and soldered up the equaliser pipe to the suction and have not noticed any difference to the performance of the unit.
    Surely, there is a technical reason for using external or internals but what is is
    Fatboy
    rbartlett's Avatar
    rbartlett Guest
    Re: Internal V's External Expansion Valves
    Where's andy when you need him?
    this will give you all you need..
    http://www.sporlan.com/10-9.pdf
    The external line compensates for the pressure drop through the evap which is why it's on the outlet when if left out will effect superheat (P & T remember) and can lead to erratic metering and/or loss of performance esp on larger evaps
    this is a subject in itself and more will follow for sure..correcting me as it goes...
    cheers
    richard
    Jun 2005
    California
    394
    The major difference is the pressure drop in the evaporator, normally
    If it exceeds 2# you would want to use an external equalized valve
    An externally equalized TEV may be used for all
    refrigeration applications. It provides no operational disad-
    vantages with respect to an internally equalized valve other
    than requiring an external equalizer line be connected.
    With both internal and external evaporators, pressure is
    transmitted to the underside of the
    valve diaphragm by one of two methods. If the valve is
    internally equalized, the evaporator pressure at the valve
    outlet is transmitted to the diaphragm via a passageway
    within the valve body or through a clearance around the
    pushrods. If the valve is externally equalized, the under-
    side of the valve diaphragm is isolated from the valve outlet
    pressure by the use of packing material around the
    pushrods or with pushrods which are closely fitted.
    Evaporator pressure is transmitted to the diaphragm by a
    tube connecting the suction line near the evaporator outlet
    to an external fitting on the valve. The external fitting is
    connected to a passageway which leads to the underside of
    the valve diaphragm. For a full understanding go here:
    May 2005
    Australia
    83
    63
    Don't ever cap off an ext equalised tx valve and use it as an internal valve. With the internal equalised TX valve the pressure at the valve outlet (or evap inlet) is transmitted to the TX valve diaphragm via a passage way within the valve or through clearance around the push rods. On an externally equalised TX this pressure is isolated from the diaphragm. Instead the suction pressure is transmitted to the diaphragm via the external equaliser line. Cap off the external port and the valve does not sense the evap pressure.
    Whenever an internal TX is used on an evap in which there is a pressure drop exceeding 20kPa then the pressure at the evap outlet will be less than the pressure operating under the diaphragm resulting in increased superheat with "starving of the evap." This is particularly severe when a distributor is fitted to the TX. Fitting an external TX prevents the evap being "starved"
    100% is possible 100% of the time
    rbartlett's Avatar
    rbartlett Guest
    many thanks
    you are of course right
    cheers
    richard
    May 2005
    Australia
    83
    63
    I knew you knew that Richard..you just probably had a hard day directing services there......
    rbartlett's Avatar
    rbartlett Guest
    we just had a mini heatwave and the workload has gone through the roof..plus ..well you know the usual....oh and I just got baned from a forum and was trying to find out why :-/
    anyway many thanks for highlighting my stupidity ;-)
    cheers
    richard
    May 2005
    Australia
    83
    63
    well you corrected your post so I did mine too...what forum you been banned from....
    rbartlett's Avatar
    rbartlett Guest
    I'm well into the old conspiracy stuff and david icke banned me ;-))
    cheers
    richard
    Dec 2004
    Australia
    52
    519
    Once saw a problem concerning this.
    Coolroom in a bakery had an old R12 condensing unit connected to a Buffalo Trident evaporator. TX valve was internally equalized and working fine for many years.
    Compressor burnt out and was replaced with a new hermitique R22 condensing unit and the installing engineer replaced the TX with an internally equalized R22 type.Unit was cooling but not properly
    No matter what he did he could not get it to feed properly.Even went to the extreme of putting a much larger than normal orifice in it.I came down and checked the super heat, room temp about 5 degrees C.Super heat was about 14 degrees at bulb of TX.
    After consulting the suppliers of these evaporators discovered that upon commisioning you have a choice of two orifices R12 and R22. These extra orifices are installed into the distributor and because of originally being R12 this was causing the R22 internal valve not to feed correctly.
    Installed external R22 valve and correct TX valve orifice.No problems superheat perfect.
  1. Soldering Expansion Valves
    By Abe in forum Domestic
    Last Post: 18-06-2006, 01:07 AM
  2. VRV expansion devices.
    By Markie in forum Air Conditioning
    Last Post: 14-04-2006, 07:20 AM
  3. Expansion
    By alesindo in forum Fundamentals
    Last Post: 30-07-2005, 09:16 AM
  4. help required in locating expansion valve power head
    By Tejbir Singh in forum Trouble Shooting
    Last Post: 10-12-2004, 02:38 PM
  5. Expansion valves
    By Martin in forum Technical Discussions
    Last Post: 13-04-2003, 04:50 AM