    So how does a provision refrigeration plant work? With 3 "FRIDGES"
    I am trying to make a schematic of a provision refrigeration system. Which is running 2 compressors and has 3 fridges. It has to be a simple drawing, with no refrigerant types, hi - low pressure cutouts etc..
    Until now I have made a schematic like this:
    But it looks like it will not work this way, as we know the temperature depents on pressures. In my schematic the pressures in every fridge are the same = same temperatures in each fridge.
    or there is a possibility to fit different size TX valves into each line to achieve different temperatures?
    Thanks guys
    Feb 2011
    EU
    7
    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"
    Can anyone please also comment what have to be the evaporation temperatures of the refrigerant in each evaporator to reach temperatures as stated? -20C, +2C and +10C. If we use for example R404 refrigerant.
    Jun 2009
    North East England
    712
    evaporation temp is 5 degrees lower than setpoint regardless of refrigerant type under normal circumstances you could use evaporator pressure regulators (EPR) to control your temp rather than expansion valves, you provide constant liquid refrigerant to the EPR which you pre set to your desired temp
    A sample diagram is here with all of the parts...
    http://www.sporlanonline.com/5-180_072010.pdf
    Also for documentation on the various components see here also...
    http://www.sporlanonline.com/literature.shtml
    Feb 2011
    EU
    7
    Thanks guys, my system has to be with a TXV, rather than with EPR.
    From which aspect does the boiling point depend on, and what does it mean "R-134 boling point -26,2C"
    Jun 2009
    North East England
    712
    water boils and begins to have a latent heat change at 100c water-steam
    R134a does the same exept liquid to vapour at -26.6c
    Apr 2008
    215
    Use the EPR's with TXV's
    -http://www.sporlanonline.com/90-20.htm
    Norway
    1,043
    4
    First you need to add more valves
    mark 1 on the drawing: you need evaporating pressure regulators on the suction of the two cold (3*C) and cool (10*C) rooms, because they have a higher evaporating pressure than the freezing room.
    http://www.danfoss.com/Products/Cate...e502a4f50.html
    mark 2 on the drawing: You need a non return valve on the suction of the freezing room, this to prevent refrigerant from migrating to the freezing room evaporator when the temperature controller to that room closes the solenoid valve.
    using R-404a as a refrigerant
    (ms paint edit )
    Bonus points: if the freezing and cool room has reached it's temperature and the solenoids are closed, but the compressor is to big to run the cold room alone and keeps pumping down. You can rig the wiring so that the freezing room solenoid is activated (as long as it is not in a defrost cycle), this should give the compressor enough capacity to keep running and be able to maintain the temp in the cold room.
    -Cheers-
    Tycho
    Apr 2008
    Southampton, England
    49
    1,023
    Can't you have one condenser with NRV in compressor discharge lines.
    More bonus points for noting capacity of rooms. The lowest temp room should be about 60% of the load on the system. This way the 2 other rooms reach temp and close LLSV then the suction pressure drops and the low temp room starts to pass refrigerant through the NRV as Tycho suggests. That's the theory I've read for 2 different rooms on 1 system so I think it would follow for 3.
    Take a butchers at the Danfoss website. I think it's mentioned in Fitters Notes.
    Cheers,
    Andy.
    Norway
    1,043
    4
    Quote Originally Posted by Tayters View Post
    Cheers,
    Andy.
    You could do with 1 condenser as you said, but if it is for a provision plant on a ship that spends a long time at sea, they will have a "standby" compressor unit.
    On supply ships for the oil industry they also charge both compressor units with enough ***** to run the system, so if a condenser starts leaking, they can seal that one out of the system and start the other one with no downtime.
    On fishing vessels they have two units, but only enough ***** to run one at a time.
    -Cheers-
    Tycho
    Jul 2011
    Malaysia
    7
    Do anyone know how to properly to do compressor sizing? 3 rooms have different evaporating temp. Condensing temp is around 40 degC. Let say +10 room required cooling is 10000 btu/h, +2 room at 12000 btu/h and -20 room at 15000 btu/h.
    Apr 2006
    55
    1,908
    30
    Off topic - needed removing
    Jul 2001
    Sydney, Australia
    753
    Quote Originally Posted by james10 View Post
    Quote Originally Posted by SchoolBoy View Post
    Reading this thread is like the blind leading the blind.
    ...and she said "give it to me you big fridgie"
    Jul 2007
    Australia
    1,845
    Hey 750, How's it going?
    I've been away for a month or two sorting out the calibre I need for the future hole in my head.
    What have you been up to?
    tycho was right wasn't he?
    edit: duh EPRs needed of course on the med temps, nothing needed for the freezer (except a CPR)
    beep boop bop, I am a robot that reads fault codes, voltages, amps, diodes, thermistors etc in sh1tty domestic a/c - refrig
    Apr 2006
    55
    1,908
    30
    Evening Paul
    or I should say Morning,
    I normally find systems with multi evaps, require 'EPR's on the chilled sections to prevent them freezing the produce & 'LLS' on every circuit to shut them down on their stat's ...
    R's chillerman
    Jul 2007
    Australia
    1,845
    What's a chiller?
    Pretty sure I worked on one in 1993.
    Yeah I figured the EPR out myself.
    Sorry, normally late at night when I post here
    Apr 2006
    55
    1,908
    30
    Quote Originally Posted by paul_h View Post
    Yeah ok
    Have seen alot of your posts, lots of common sense, educating us older folk,
    R's chillerman
  1. What is the best "reasonably" priced book for Learning Refrigeration?
    By TheFridgeMan in forum Refrigeration Books
    Last Post: 21-06-2010, 12:11 PM
  2. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Last Post: 02-03-2008, 06:10 PM