03-08-2011, 01:32 PM #1
denco ccu trouble
Hi,can anyone help I have several ccu's with humidifier faults arrived on site found existing bottles scaled up changed all tried to reset faults on trend excite front end. now 4 bottles dont even fill and the others are working but still show hum faults changed fill valves,checked water to unit ok.any help much obliged.model. D94. FVH and D54AVH.
-
04-08-2011, 01:00 PM #2
Re: denco ccu trouble
I would suspect you have a fault code on the hum board.
Can you confirm what lights are flashing and the sequence.
ThanksRob Woodworth
GEA Denco Technical Support
rob.woodworth@geagroup.com
-
16-08-2011, 10:11 AM #3
Re: denco ccu trouble
Hello rob,thanks for reply,on hum boards I have a constant green led and a red led flashing 7 and then 8 times continuosly.cheers, ali.
-
22-08-2011, 09:24 AM #4
Re: denco ccu trouble
Okay, it sounds like the hum board is in fault, drop me a email and i will send you the O&M for the hum board as its too big to attach here.
rob.woodworth@geagroup.comRob Woodworth
GEA Denco Technical Support
rob.woodworth@geagroup.com
-
22-08-2011, 03:35 PM #5
Re: denco ccu trouble
email sent.
Rob Woodworth
GEA Denco Technical Support