    city multi with g 50



    i have a mitsi city multi with a g50 controler set the units up on the time clock with a set temp of 23 when the units switch on 2 of the units start with a set point of 19 the others start at 23 any idears



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: city multi with g 50

    check the timer schedule for each unit and omit the set temp otherwise it will start up at 19 each day

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: city multi with g 50

    Check which schedule pattern is selected and check if the set temp is locked at 19
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: city multi with g 50

    stufus is right, check your patterns P1 to P3 and also P4 (Prohibit scheduler).
    G50 patterns.jpg