10-03-2011, 08:04 PM #1
city multi with g 50
i have a mitsi city multi with a g50 controler set the units up on the time clock with a set temp of 23 when the units switch on 2 of the units start with a set point of 19 the others start at 23 any idears
-
10-03-2011, 08:56 PM #2
Re: city multi with g 50
check the timer schedule for each unit and omit the set temp otherwise it will start up at 19 each day
-
10-03-2011, 10:07 PM #3
Re: city multi with g 50
Check which schedule pattern is selected and check if the set temp is locked at 19
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
11-03-2011, 04:00 AM #4
Re: city multi with g 50
stufus is right, check your patterns P1 to P3 and also P4 (Prohibit scheduler).