    Split valve



    Hi

    A tech student of mine is installing a Mini split which has 900g of fluid inside acording to service manual.

    After tubes were assembled and manifold linked to low side valve, valve was open
    1/4 counterclockwise, and vaccum pump turned on.

    Instead of vaccum, the fluid output by the vaccum pump.

    I will tell him to close the valve, but I wonder if tubes will be vacuumed this way.

    Any help will be welcome

    Thanks


    Moises


    .



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Split valve

    You're not supposed to open the valves. You as supposed to use the vacuum pump to make vacuum on the indoor unit and your piping, not the outdoor unit. So the valves should have been kept closed.

    you're going to have to reclaim the whole system now with valves open, evac it with valves open, and charge with 900g of refrigerant after evac now.

  3. #3
    Join Date
    Dec 2008
    Location
    Brazil
    Posts
    106
    Rep Power
    16

    Re: Split valve

    Thank you Paul

    I was going to tell him to keep the valve close, but I also will have to explain him how piping will get vacuumed if nothing is open.

    Could the low site valve be schreader valve ?

    Moises

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Split valve

    If he is your tech student, are you an authorised teacher of the refrigerant trade?

    Did no one read the installation instructions?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,024
    Rep Power
    36

    Re: Split valve

    Quote Originally Posted by Acrisoft View Post
    Thank you Paul

    I was going to tell him to keep the valve close, but I also will have to explain him how piping will get vacuumed if nothing is open.

    Could the low site valve be schreader valve ?

    Moises
    Not quite sure what you mean here. I take it you have 2 valves with an Allen key head and an access port on the suction valve.

    Smaller units normally only have an access port on the suction valve only. Larger systems may have access ports on both valves.
    As already posted, you need to vac from the ports then open the valves up.
    Health and safety first..........unless I'm in a hurry.

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: Split valve

    Is this a wind up or a trick question?
    Who exactly is the teacher and who is the student?
    If you are the teacher should you not know the basics?
    No pressure test??
    Tell the student to sign up to R.E. and put his tuition fees into a beer fund for the members
    Cheers
    Stu
    Last edited by stufus; 23-02-2011 at 10:00 PM.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

Similar Threads

  1. The difference between an EPR valve and a CPR valve?
    By kengineering in forum Technical Discussions
    Replies: 7
    Last Post: 05-02-2010, 07:47 AM
  2. Split 3 way valve
    By Acrisoft in forum Air Conditioning
    Replies: 6
    Last Post: 29-05-2009, 11:58 PM
  3. Replies: 18
    Last Post: 15-04-2009, 08:42 PM
  4. Single-split VS Multi-split
    By kitmel in forum Air Conditioning
    Replies: 1
    Last Post: 13-02-2009, 03:48 PM
  5. Replies: 2
    Last Post: 06-02-2009, 07:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •