22-02-2011, 01:15 PM #1
Split valve
Hi
A tech student of mine is installing a Mini split which has 900g of fluid inside acording to service manual.
After tubes were assembled and manifold linked to low side valve, valve was open
1/4 counterclockwise, and vaccum pump turned on.
Instead of vaccum, the fluid output by the vaccum pump.
I will tell him to close the valve, but I wonder if tubes will be vacuumed this way.
Any help will be welcome
Thanks
Moises
.
-
22-02-2011, 01:29 PM #2
Re: Split valve
You're not supposed to open the valves. You as supposed to use the vacuum pump to make vacuum on the indoor unit and your piping, not the outdoor unit. So the valves should have been kept closed.
you're going to have to reclaim the whole system now with valves open, evac it with valves open, and charge with 900g of refrigerant after evac now.
-
22-02-2011, 02:03 PM #3
Re: Split valve
Thank you Paul
I was going to tell him to keep the valve close, but I also will have to explain him how piping will get vacuumed if nothing is open.
Could the low site valve be schreader valve ?
Moises
-
22-02-2011, 11:18 PM #4
Re: Split valve
If he is your tech student, are you an authorised teacher of the refrigerant trade?
Did no one read the installation instructions?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
23-02-2011, 09:50 PM #5
Re: Split valve
Not quite sure what you mean here. I take it you have 2 valves with an Allen key head and an access port on the suction valve.
Smaller units normally only have an access port on the suction valve only. Larger systems may have access ports on both valves.
As already posted, you need to vac from the ports then open the valves up.Health and safety first..........unless I'm in a hurry.
-
23-02-2011, 09:58 PM #6
Re: Split valve
Is this a wind up or a trick question?
Who exactly is the teacher and who is the student?
If you are the teacher should you not know the basics?
No pressure test??
Tell the student to sign up to R.E. and put his tuition fees into a beer fund for the members
Cheers
StuLast edited by stufus; 23-02-2011 at 10:00 PM.
Tool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
Similar Threads
-
The difference between an EPR valve and a CPR valve?
By kengineering in forum Technical DiscussionsReplies: 7Last Post: 05-02-2010, 07:47 AM -
Split 3 way valve
By Acrisoft in forum Air ConditioningReplies: 6Last Post: 29-05-2009, 11:58 PM -
3 single split units or one multi split - consumer advice needed
By kok in forum Air ConditioningReplies: 18Last Post: 15-04-2009, 08:42 PM -
Single-split VS Multi-split
By kitmel in forum Air ConditioningReplies: 1Last Post: 13-02-2009, 03:48 PM -
Motorized Ball valve versus Globe valve for modulating application
By Sridhar1312 in forum IndustrialReplies: 2Last Post: 06-02-2009, 07:35 PM