    Daikin outdoor main supply MCB triped



    I have Daikin 28hp, VRVIII system with 13 indoor units.Before 15 days , outdoor main supply MCB triped due to that all indoor units remote shows "U4" error.switch on the supply, system running satisfactory.

    Today also outdoor unit main MCB triped.I dont understand wheather it was voltage flucution fault or there is problem in outdoor model due to that main supply MCB trip.

    please sugest, which is the possible reason for outdoor Main supply MCB triping.



  2. #2
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    What size is the mcb? Does it trip at a particular time of day? Have u seen all comps and fans run?

  3. #3
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Quote Originally Posted by ktm View Post
    What size is the mcb? Does it trip at a particular time of day? Have u seen all comps and fans run?
    thanks for reply

    Legrand make MCB specification :415v,C63 Icu -10000ka,10KA &
    another attached 0.1A,100mA

    No it is not trip at particual time ( may be at starting period)

    I have not seen all comps and fans run
    Last edited by sachin230; 10-11-2010 at 11:25 AM.

  4. #4
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Try run system on full heat or full cool so all the fans and comps will run. Could b a problem with a fan or one if the compressors. No water in the isolator switch?

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Daikin outdoor main supply MCB triped

    The thing that trips, is it a MCB or an RCD?
    The 100ma makes me wonder if it is an RCD and its tripping due to earth leakage currents caused by the inverter circuit.

    Is the a new installation or has it been working for a while?

    Jon

  6. #6
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Thanks jon
    this is new installation before one year but this problem start from last one month.(four different times supply mcb tripped)
    I think It is RCBO

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Daikin outdoor main supply MCB triped

    I think inverters can make rcd's trip even when working correctly, it would help if you could fine out whether it was over current or earth leakage that was causing the tripping.

  8. #8
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Please guide me How to find the inverter leakage current and earth leakage.?
    what is the procedure to find the invertor leakage current and earth leakage?

  9. #9
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    your feedback much appreiciated

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Daikin outdoor main supply MCB triped

    Quote Originally Posted by sachin230 View Post
    Please guide me How to find the inverter leakage current and earth leakage.?
    what is the procedure to find the invertor leakage current and earth leakage?
    I don't know! Its not a problem i have seen personally.

  11. #11
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Here are notes I put together for a level 3 lecture on electrical safety.

    RCD Ratings other than the standard 30mA

    100mA
    Socket outlets of rating exceeding 32 A in agricultural locations.
    300mA
    At the origin of a temporary supply to circuses etc.
    Where there is a risk of fire due to storage of combustible materials
    All circuits (except socket outlets) in agricultural locations.
    Inverter drive systems such as found on AC systems.
    500 mA
    Any circuit supplying one or more socket outlets of rating exceeding 32 A, on a construction site.

  12. #12
    javed's Avatar
    javed Guest

    Re: Daikin outdoor main supply MCB triped

    you should check machine indoor and outdoor unit communication wire.
    i had same problem .

  13. #13
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Is your problem solved ? how?

    I checked indoor unit and outdoor unit communication it is ok.

    sometimes RCBO triped, & due to that indoor unit shows "U4"error.

    Tripping not continous.where to arrest the the problem

  14. #14
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    Quote Originally Posted by sachin230 View Post
    Is your problem solved ? how?

    I checked indoor unit and outdoor unit communication it is ok.

    sometimes RCBO triped, & due to that indoor unit shows "U4"error.

    Tripping not continous.where to arrest the the problem
    This is your problem Legrand make MCB specification :415v,C63 Icu -10000ka,10KA &
    another attached 0.1A,100mA

  15. #15
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    I dont understand (100MA )

  16. #16
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    The RCD or RCBO is designed to be sensitive to 100mA leakage current - you need one rated at 300mA because the leakage current caused by an inverter for used on mini plits and VRV system is up nearer 200mA at peak.

    If your system's loop impedance could permit the breaker to still trip within the time stipulated by your regulations or your earthing system was unreliable then you would not even use a breaker but would be forced to use an RCD or RCBO. In which case it should be selected for 300mA leakage current.

  17. #17
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: Daikin outdoor main supply MCB triped

    How often does it trip? once a day once a month? It sounds to me like a compressor.
    If it is dooing it every couple of days and the load on the system is, it would make sennse.

  18. #18
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Daikin outdoor main supply MCB triped

    It trip once a month

Similar Threads

  1. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  2. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  4. Daikin or Mitsubishi
    By eloroncedark in forum Air Conditioning
    Replies: 25
    Last Post: 11-08-2008, 03:01 PM
  5. Daikin 7kW Cassette +supply duct to small office
    By Makeit go Right in forum Air Conditioning
    Replies: 6
    Last Post: 12-12-2007, 03:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •