10-11-2010, 07:34 AM #1
Daikin outdoor main supply MCB triped
I have Daikin 28hp, VRVIII system with 13 indoor units.Before 15 days , outdoor main supply MCB triped due to that all indoor units remote shows "U4" error.switch on the supply, system running satisfactory.
Today also outdoor unit main MCB triped.I dont understand wheather it was voltage flucution fault or there is problem in outdoor model due to that main supply MCB trip.
please sugest, which is the possible reason for outdoor Main supply MCB triping.
-
10-11-2010, 10:08 AM #2
Re: Daikin outdoor main supply MCB triped
What size is the mcb? Does it trip at a particular time of day? Have u seen all comps and fans run?
-
10-11-2010, 11:22 AM #3
Re: Daikin outdoor main supply MCB triped
Last edited by sachin230; 10-11-2010 at 11:25 AM.
-
10-11-2010, 01:17 PM #4
Re: Daikin outdoor main supply MCB triped
Try run system on full heat or full cool so all the fans and comps will run. Could b a problem with a fan or one if the compressors. No water in the isolator switch?
-
10-11-2010, 01:39 PM #5
Re: Daikin outdoor main supply MCB triped
The thing that trips, is it a MCB or an RCD?
The 100ma makes me wonder if it is an RCD and its tripping due to earth leakage currents caused by the inverter circuit.
Is the a new installation or has it been working for a while?
Jon
-
11-11-2010, 07:14 AM #6
Re: Daikin outdoor main supply MCB triped
Thanks jon
this is new installation before one year but this problem start from last one month.(four different times supply mcb tripped)
I think It is RCBO
-
11-11-2010, 10:24 PM #7
Re: Daikin outdoor main supply MCB triped
I think inverters can make rcd's trip even when working correctly, it would help if you could fine out whether it was over current or earth leakage that was causing the tripping.
-
16-11-2010, 05:49 AM #8
Re: Daikin outdoor main supply MCB triped
Please guide me How to find the inverter leakage current and earth leakage.?
what is the procedure to find the invertor leakage current and earth leakage?
-
17-11-2010, 11:23 AM #9
Re: Daikin outdoor main supply MCB triped
your feedback much appreiciated
-
17-11-2010, 02:40 PM #10
-
17-11-2010, 04:00 PM #11
Re: Daikin outdoor main supply MCB triped
Here are notes I put together for a level 3 lecture on electrical safety.
RCD Ratings other than the standard 30mA
•100mA
–Socket outlets of rating exceeding 32 A in agricultural locations.
•300mA
–At the origin of a temporary supply to circuses etc.
–Where there is a risk of fire due to storage of combustible materials
–All circuits (except socket outlets) in agricultural locations.
–Inverter drive systems such as found on AC systems.
•500 mA
–Any circuit supplying one or more socket outlets of rating exceeding 32 A, on a construction site.
-
19-11-2010, 02:01 PM #12
Re: Daikin outdoor main supply MCB triped
you should check machine indoor and outdoor unit communication wire.
i had same problem .
-
22-11-2010, 06:54 AM #13
Re: Daikin outdoor main supply MCB triped
Is your problem solved ? how?
I checked indoor unit and outdoor unit communication it is ok.
sometimes RCBO triped, & due to that indoor unit shows "U4"error.
Tripping not continous.where to arrest the the problem
-
22-11-2010, 08:49 AM #14
-
24-11-2010, 07:08 AM #15
Re: Daikin outdoor main supply MCB triped
I dont understand (100MA )
-
24-11-2010, 07:58 AM #16
Re: Daikin outdoor main supply MCB triped
The RCD or RCBO is designed to be sensitive to 100mA leakage current - you need one rated at 300mA because the leakage current caused by an inverter for used on mini plits and VRV system is up nearer 200mA at peak.
If your system's loop impedance could permit the breaker to still trip within the time stipulated by your regulations or your earthing system was unreliable then you would not even use a breaker but would be forced to use an RCD or RCBO. In which case it should be selected for 300mA leakage current.
-
24-11-2010, 06:55 PM #17
Re: Daikin outdoor main supply MCB triped
How often does it trip? once a day once a month? It sounds to me like a compressor.
If it is dooing it every couple of days and the load on the system is, it would make sennse.
-
30-11-2010, 11:34 AM #18
Re: Daikin outdoor main supply MCB triped
It trip once a month
Similar Threads
-
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM -
Daikin or Mitsubishi
By eloroncedark in forum Air ConditioningReplies: 25Last Post: 11-08-2008, 03:01 PM -
Daikin 7kW Cassette +supply duct to small office
By Makeit go Right in forum Air ConditioningReplies: 6Last Post: 12-12-2007, 03:41 AM