    Hi all....especially the oldies who might have an answer!
    Just been to a local butchers to look at one of his coldrooms. Gauge (LP) pressure with system off did not tally with what I was expecting (R12 ?) .....pressure was too high.
    A quick butchers (no pun intended!) at the TEV showed it was on Methyl Chloride.
    This is my first run in with the gas, but I do know that it is one to be wary of...toxicity and flammable......turns out the system has been in since shop was built in the '60s. The old fridgidare condensing unit is still working sweet
    Symptoms at first glance were possible shortage of gas, but sight glass was clear, so a quick pump down showed charge was probably OK and pointed to the TEV.
    Adjusting the superheat has temporarily got the system cooling again, but now to the question of what to do next.
    Are any of the currently available TEV's liable to work satisfactorily with the R40? (R12 for example).
    What oil is likely to be in the system?.....Mineral?
    Any suggestions for a drop in conversion? I haven't (as yet) found a P-T chart for R40 as my books don't go back that far, so direct comparison is currently difficult, but I guess that R12 might be close so possibly a R12 drop in would work.
    Thanks, ECM
    Jun 2001
    N.Ireland
    1,630
    Re: R40 (Methyl Chloride) Alternatives
    Quote Originally Posted by Electrocoolman View Post
    Thanks, ECM
    Helllo Electrocoolman
    R12 would often be charged into methyl chlorine systems, I would try an R12 valve. I have seen bottles of methyl chlorine in BOC a few years back, so your system should still be viable. Mineral oil, 4GS from memory.
    Kind Regards Andy D
    Sep 2008
    Newcastle upon tyne
    75
    80
    Hello
    I can remember working back in the 60s on Methyl Chloride and SO2 systems but cant remember retrofitting.
    Can remember that it can get very dangerous somehow if system is retrofitted and it is not perfectly clean.
    I would make more enquiries on this 1.
    There was a definite risk retro fitting these gases.
    Aww
    Oct 2006
    Bucks, U.K.
    71
    604
    Thanks Andy and Alan,
    Although I've not tried to get hold of any Andy, you might be correct in thinking that its still available. Not sure whether its covered under Montreal Protocol as it doen't contain Fluorine. Does anyone know anything further regarding this point?
    Thats a good point Alan regarding retrofitting. I'll have to do more research.
    Nov 2006
    708
    I know its very potent stuff to your respirator system and that its heavier than air
    please tread carefully
  1. calcium Chloride with NH3 absorption
    By happyjay75 in forum Refrigeration Books
    Last Post: 11-09-2008, 11:53 AM
  2. calcium Chloride with NH3 absorption Area
    Last Post: 28-07-2008, 09:18 PM
  3. Insulation alternatives
    By fishmonger in forum Commercial
    Last Post: 02-01-2007, 03:09 PM
  4. Can I use calcium chloride in propylene system?
    By joanna in forum Hydrocarbons
    Last Post: 23-12-2006, 10:18 PM
  5. Methol Chloride
    By Andy in forum Refrigerants
    Last Post: 03-08-2002, 09:44 AM