    Oct 2009
    Pietermaritzburg
    40
    24000Btu Rotary Compressor overheating
    Hi, i recently was ordered to attend to a midwall split unit that wasnt working. Compressor was not pumping. Changed the compressor, pulled a vacuum, charged unit and unit ran for about 5 mins then compressor stopped and was very hot. The unit is a Samsung. I thought there might be a blockage by the capilliary tubes, i flushed the whole unit, but there wasnt any blockages. Discharge pressure was around 150 psi and suction was going into a vacuum. Thought that i had undercharged unit but that wasnt the case. Please help. The unit is all single phase 220v. And its a R22 system.
    3,853
    Re: 24000Btu Rotary Compressor overheating
    I have seen some strainers block up on basic R22 splits, i could blow through with nitrogen ok but once i put some R22 back in it blocked up again.
    In the end i replaced the strainer with a small 032 drier as the system was a cooling only unit and it worked ok.
    I think it is because of the oil going waxy.
    Jon
    Service valves fully open ?
    Apr 2009
    israel
    778
    Quote Originally Posted by tudorice View Post
    is the 4 way valve ok???
    check the strainer!
    good luck
    Jun 2009
    United States
    59
    10
    Ya, I was going to say, check the reversing valve as well.. You have a restriction, use process of elimination even if you have to install service ports at key spot in suction line.
    If the compressor gos into an immidiate vacuume its probably the four way valve.
    OH... lol, when you replaced the compressor did you use a new piece of hard drawn copper and forget to remove the rubber plug????
    Oct 2009
    Pietermaritzburg
    40
    hey guys thanks for the help, I checked the wiring again on the compressor terminals (thinking that maybe i had got them the wrong way). Checked again for blockages, found none, its a cooling only machine, doesnt have any strainers. And i found the problem. Which i am very embarrased about. On some samsung remotes there is a built in thermometer and u have to adjust the temp to see the set point temp. whilst i was away someone adjusted it to above the room temp, so the compressor wasnt running for long enough, and hence why i couldnt charge the unit properly, leaving me to think that there was enough gas in the system and that there might be a blockage or that the wiring on the compressor was wrong. Big my bad.
    3,853
    Pleased you found them problem!
    Jon
    Glad problem is resolved but - you should really weigh in the gas charge if possible; it's much safer.
  1. Rotary Compressors
    By hoolagan in forum History of Refrigeration
    Last Post: 15-02-2011, 11:59 AM
  2. rotary type replacement compressor in place of a piston type unit
    By frozenpal2010 in forum Air Conditioning
    Last Post: 06-09-2010, 05:37 AM
  3. Rotary compressor a good choice in VRF?
    By K.R.Iyer in forum New Technologies
    Last Post: 04-06-2009, 06:08 PM
  4. piston type vs rotary
    By friocold2008 in forum Air Conditioning
    Last Post: 28-05-2009, 08:38 AM
  5. Dehumidifiers and Rotary Compressors
    By Pete L in forum Commercial
    Last Post: 16-10-2007, 11:06 PM