    evaporator problem



    I have a r-22 3 ton heatcontroller evaporator that kept freezing up. I removed piston and installed a 3 ton xpansion valve. I notice all 6 spider tubes getting wet yet only 4 0f the 6 3/8" suction tubes leading into the 3/4" suction manifold are getting wet. I put the sensing bulb in warm water and the valve opens up , but those 2 tubes still remain dry. Could it be a partial restriction in those spider tubes.



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: evaporator problem

    Billdozer, is this a freezer room or coldroom and does the evaporator partially ice up, say bottom 1/3 or fully ice?..mike

  3. #3
    Join Date
    Dec 2009
    Location
    new york
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: evaporator problem

    residential A/C system its no longer freezing up now, but 1/4 of the coil is dry

  4. #4
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: evaporator problem

    I have seen restrictions where the tubes are brazed into the distributor. Some of the braze ends up in the tubes.Would need more info though. Superheat/subcooling temps splits etc etc etc

  5. #5
    Join Date
    Dec 2009
    Location
    new york
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: evaporator problem

    pressures 170 over 58
    outdoor temp-80f
    indoor wet bulb-58f
    indoor temp-68f
    return air temp-69f
    supply air temp-55f
    tempreture suction line @ service valve 56f
    indoor/outdoor coils sparkling clean.
    no pleated filters.
    removed sensing bulb off TXV and tested in both ice and warm water and valve reacted accordingly.
    compressor rated for 13 RLA unit running at 10.5, System has no leaks pressurized for 1 month at 250 PSI and held. Vacuumed for 5 hours and microned to 400, held up to 700 for a hour. New liquid line filter dryer and sight glass with moisture indicator. Periodic bubbling, valve does not hunt. 1 more thing i would like to mention the unit is cooling the first floor but the return is in basement, is it possible that the colder air in basement throttling my TXV and giving me my high super heat.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: evaporator problem

    Did you fitted externally equalized TXV, and is distributor placed vertically? Could you make photo of that TXV-distributor setup?

  7. #7
    Join Date
    Dec 2009
    Location
    new york
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: evaporator problem

    yes xternal equalizer and b4 sensing bulb & the bulb is mounted horizontally @ 8:00

  8. #8
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: evaporator problem

    Here's my 2 cents worth. If all your technical readings are still holding steady, and the rated RLA is truly for the compressor only, you seem to be running head pressure somewhat low for R22. Watch your amps and add some ***** to reach 220-230. Your coil sounds like it is frosting from bottom up and dist. tubes are starving. All of the other bases have been covered so give this a try. Hope it helps. Good luck.
    Don't leave it like you found it.....Leave it like it should be !!!

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: evaporator problem

    Your superheat at service valve is (56°F-38°F)=18°F. If we presume that pressure drop from evaporator to compressor (service valve) should not exceed equivalent of 4°F, you still have 14°F of evaporator superheat. That is high for R22. It should be around 10°F.
    Check that TXV (if adjustable) is at factory setting (measure with number of turns or with sliding ruler).

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: evaporator problem

    Quote Originally Posted by billdozza View Post
    is it possible that the colder air in basement throttling my TXV and giving me my high super heat.
    Nope, superheat will remain at preset value if you have liquid refrigerant at valve inlet and if TXV is fully functional, no restriction and properly installed.

  11. #11
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: evaporator problem

    Hi there,

    If two of the distributor tubes behave differently then there is a problem of pressure drop difference between those tubes. As mentioned be by joe magee, it could be partial restriction in the tubes or the length of the tubes are not the same which gives different pressure drops.
    Cheers
    Even Einstein Asked Questions