    Crankcase Pressure Regulator Valve
    HI. I`m fairly new to this.but does any one know what the Crankcase PRV is supposed to set at ? and if not set correctly would it cause compressor to ice up on the end when system is going thru defrost cycle. This is for a 5 horse power copeland hermatic compressor used for a reach in grocery store freezer display. 404A *****
    midnight50's Avatar
    midnight50 Guest
    Re: Crankcase Pressure Regulator Valve
    the way u need to set it up is to use your gauges and put about 100psig into the suction line and adjust valve until u get compressor to RLA amps
    Jun 2010
    89
    why is my suction line freezing up and compressor sweating when it goes into hot gas defrost? I thought it was because the PRV was not set right
    5,667
    Have a read up on CPR vavles here http://www.parker.com/portal/site/PA...RCRD&stpoint=B
    Oct 2006
    1,843
    Quote Originally Posted by jakb21599 View Post
    You need to understand what is does first.
    There are a few pressure control valves that can be
    fitted to the suction but they do different
    things for different aplications.
    There are crankcase pressure regulators (CPR) and then
    there are evaporator pressure regluators (EPR), to name two.
    Do not confuse the two..
    The CPR protects the compressor from too much suction pressure
    Some systems with multiple evaporators and comps use them to
    stop the suction pressure getting too high. It is basicaly to protect
    the comp in extreme situations like defrost and startup.
    The EPR regulates the pressure inside the evap purly
    for temp control in the evap itself.
    Nether are designed to prevent liquid but both will affect pressures
    and therfore temps inside the suction and back to the comp.
    You need to find why your suction is freezing. Do not think that a
    freezing suction automatically means liquid. It can mean the suction
    is below freezing and that will happen with low temp and some medium
    temp systems. Remember that the evap temp of a 404 freezer will be
    about -35 degC ( - 30 degF in your money ) so the suction will freeze
    up with just suction vapour returning.
    All the best
    taz
    Jun 2010
    89
    thanks for your help guys
    Feb 2008
    adelaide sth.oz
    1,015
    you have liquid coming back
    Jun 2007
    South Africa
    66
    120
    Suction line freezing and compressor sweating does not indicate liquid flood back.
    What is the suction superheat?
    Semi Hermetic Compressors can show white frost all over the compressor motor area, up to close to the heads, without liquid coming back.
    Determine suction superheat, which should be 5 deg C minimum.
    I am not always right, but I'm never wrong!
    Feb 2008
    adelaide sth.oz
    1,015
    if hes got frosting after the cpr during defrost superheat of tx has nothing to do with it.
    5 deg c superheat in low temp system lol
    Feb 2009
    Australia
    272
    jakb21599,
    Frosting on the suction after the Crankcase Pressure Reg on hot gas defrost is normal,i have seen it a on all the hot gas defrost systems i installed,,,it's normal,,,,set the C/P/Reg at compressor full load amps,,,ignore the pressures.
    Lawrie
  1. How to Design Refrigeration Systems
    By US Iceman in forum Fundamentals
    Last Post: 24-07-2008, 04:27 PM
  2. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Last Post: 24-12-2007, 01:06 PM
  3. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Last Post: 08-03-2007, 05:34 AM
  4. Crankcase Pressure Regulator
    By Abe in forum Technical Discussions
    Last Post: 10-09-2006, 01:56 PM