    ACIS's Avatar
    ACIS Guest
    Exclamation carlyle compressor
    Currently I am a have a problem with a carlyle 6e compressor. I repaired a leak and added 150 pounds of refrigerant to the split carrier condenser with seperate receip compressors. I have a 70 psig suction / 325 psig discharge / 230 liquid pressure / 13 degree subcool / 7 degree superheat / 47 suction temp / 98 liquid temp / 210 discharge temp / 30 psig oil pressure / rated for 65 amps pulling 70 to 68 on all three legs. After some run time the compressor will start to climb to 415 and plus eventually going on and off by head pressure were my liquid pressure will remain around 250 psig. All condenser fans are operating and I am getting the correct cooling out of the evaporator system. It is a built up txv system.
    what could be the problem. I have heard of this issue being from the reed valves, but no 100 percent sure and would like to know why it would also cause this if it is possible. Thanks for you time.
    38
    Re: carlyle compressor
    Either overcharged or dirty condenser.
    Being Carrier there will a system charge stated on nameplate.
    What refrigerant is installed in system .
    Jul 2008
    London
    848
    how's that work?
    Feb 2001
    Tampa Florida
    1,076
    That should tell us something. Plugged liquid line filter, perhaps?
    38
    Hi Multi.
    too true, something will blow sooner than later, if the compressor does not die in the mean time, or the contactors errupts or all at the same time.
    I am thinking system is on 22 and cooking everything, oil, compressor. Carbon yardy yardy. Uncool.
    The O6E 's are bullet proof compressors working in there design envelop.
    Aug 2007
    Sydney
    52
    1,083
    Check out your TEV is it starved? symptoms look like partial blockage between condenser and tev. You could have overcharged for the elevated suction press and current. Is there a distributor on the evap?
    If you are down to temp and stable I think 70psi suction could be a little high.
  1. copeland scroll durability
    By Third_techtrio in forum Technical Discussions
    Last Post: 23-01-2010, 04:47 AM
  2. Catastrophic compressor failure...need info
    By bsh3239 in forum Industrial Compressors
    Last Post: 28-11-2009, 04:30 PM
  3. Replies: 3
    Last Post: 29-10-2009, 09:41 PM
  4. seized inv compressor
    By flash in forum Air Conditioning
    Last Post: 09-04-2008, 06:56 PM
  5. Compressor Capacity
    By engrkate in forum Fundamentals
    Last Post: 13-10-2006, 12:11 AM