    maneurop r22



    H i all I have a comp to change on a DX system on R22 as it is in a non running state I have a few things to figure out I have located a replacement comp that will run 22 in the meantime, now the system takes a charge of 44 Kilo any one got an idea of the standing pressure, as the comp has a leaking roto lock LS valve which is peeing oil this will be getting replaced , Now any way I can seal off the system to change this valve or is it a case of gas out if not it will have to run under monitor till the autunm when the demand drops this will be the time to change to Isceon 59 this will I have been told will operate perfectly with the mineral oil do you guys concur
    Cheers Dev



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: maneurop r22

    devlin, you have a system thats leaking you are going to have to re- claim the gas to do the job of changing the comp, so why not do that now?< then you wont loose any nasty r22<
    leaking rotalock valve? where is the leak,on the brazed joint on the pipe to the valve ,or on the stuffing gland, can you tighten it up ?
    you ask what is the standing psi. it may depend on the temp? I will have to look at my campariter to tell you that,
    or can you farward seat both liquid + suction valves, then you will ONLY loose gas from the cond, unit< or you could vac out a r22 bottle and put a line from the cond unit onto the said bottle and loose very little r22

  3. #3
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: maneurop r22

    Hi Sedgy the valve is in a vertical position and leaks from the stem you only have to touch it for it to leak from the low side service port I will have to recover from the comp and condenser frame as it;s a double sided job and will contain a lot of 22 I have not had a good look at the underside IE the stem to see if its tightenable but my thoughts are it's knacked and thanks for your reply any more thoughts are welcome,
    Dev
    Last edited by devlin maguire; 09-08-2010 at 07:32 PM.

  4. #4
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: maneurop r22

    Hi Valve has now stopped leaking the gland nut was loose (thanks sedgy) new comp arriving mid week, asI know nothing of this installs history other that the original charge 44 kilos R22 what would I expect pressure wise on both sides a ball park figure would give me a baseline It's a Dx system with a pipe run of 15 metres This is the first large system I have worked onI am more at home with cellars and walk ins so I would really appreciate some help
    Dev

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: maneurop r22

    Hi Delvin,

    From my limited R22 AC experience:

    Low side 55-60psig (-1 to 1*C)
    High Side 200 psig (ish. Condensing around the 40*C mark)

    Whe recharging with MO59 then final charge is normally about 90% of the R22 amount.
    The oil return is achieved by having a small amount (1 or 2%) of a HC which mixes with the mineral oil well and carries it back from the evaporator.

    Standing charge from a comparator at 20*C is a nats danglies below 120psig.

    Hope that help,

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  6. #6
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: maneurop r22

    Cheers tayters most helpfull
    Dev

Similar Threads

  1. Suniso 3GS instead of Maneurop white oil 160P
    By nike123 in forum Air Conditioning
    Replies: 8
    Last Post: 01-11-2010, 05:42 AM
  2. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  3. r417a maneurop r22 compressor
    By ryscaff in forum Trouble Shooting
    Replies: 4
    Last Post: 04-12-2009, 08:11 AM
  4. Maneurop compressor
    By kaskiris in forum Commercial
    Replies: 2
    Last Post: 11-11-2008, 07:31 AM
  5. Maneurop parts (EBM fan)
    By Contactor in forum Fundamentals
    Replies: 4
    Last Post: 07-08-2007, 11:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •