    using nitogen when brazing
    Never used nitrogen before while brazing.
    Say you are replacing any part on a system and say you have two joints to make, do you just hook up nitrogen and let it feed in while brazing? And when you are making up that last joint where does the nitrogen blow the contaminates out of system. And how much pressure do you feed in? Explain in detail please, I'm a little slow LOL
    Jun 2009
    North East England
    712
    Re: using nitogen when brazing
    You should purge ofn at around 2psig when brazing letting the ofn go round the full system when it comes to the last joint open a schrader or service valve on the system if you only have one connection you can use a line tap valve or dont purge on the last connection, using ofn does not blow out contaminants out of the system it displaces oxygen and prevents oxidisation on the inner walls of the tube the difference is extreme cut open a purged joint and a non-purged joint you'll be suprised
    May 2006
    Sussex
    362
    Nov 2009
    27
    OFN makes one hell of a difference to the internal surface of refrigeration grade copper when brazing, Jon. Not looked at the video link, but I've cut open an OFN joint, and a non-OFN joint after a test braze. The difference is staggering.
    Don't be fooled by the techno's who'll have you believe that handling OFN needs a qualification in quantum physics. It's no more hazardous than a pub cellar CO2 system. Make sure you have the right guages (dedicated OFN set - NOT LINE GUAGES!!) and treat it with respect.
    Using it will result in a super-clean system which will massively reduce the chances of premature comp failure, and outstanding strength / leak testing results that only a fool would ignore.
    Jun 2010
    Ireland
    168
    I'm so glad someone else asked that question. Thanks
    jonc5553's Avatar
    jonc5553 Guest
    Watched video. Thanks alot for responses
    Jun 2009
    North East England
    712
    QUOTE FROM ANDYCHILLS POST!!!!!!!!!!!!
    " Don't be fooled by the techno's who'll have you believe that handling OFN needs a qualification in quantum physics. It's no more hazardous than a pub cellar CO2 system. Make sure you have the right guages (dedicated OFN set - NOT LINE GUAGES!!) and treat it with respect."
    People are often fooled by N2,if you breath in a single lung full of nitrogen you'll hit the floor stone dead, some of the larger companies including many petro chemical sites have banned it's use for purging etc,Also in some parts of the worl it is being considered to be used for exocutions replacing toxic gases and the leathal injection
    Aug 2008
    London
    59
    ...also don't turn off the flow until the joint has cooled. Oh! and use a large flame rather than small one as excessive heat will likely result in a porous joint...
    Oct 2003
    5,630
    Quote Originally Posted by jonc5553 View Post
    The nitrogen doesn't blow out the contamination out of your tubes. It only prevents carbonizing the inner side of the tubes.
    You don't need any pressure - in fact a pressure isn't allowed - you only need a steady flow, the lowest flow possible once the tubes are full of OFN.
    You need a pressure regulator which regulates a flow and not a pressure (a flow of +/- 2 l/min is more than enough.
    In the Belgium certification (En378/2008), you must prove that you can make solders (phosphor and silver brazings) without a black inner wall. If we find one black spot due to oxygen infiltration, you can come back for this part of the exams.
    If you have a warranty case with Daikin compressors and they find carbon from soldering in the compressors, your warranty will be void
    Feb 2006
    derbyshire
    610
    thats a bit rich from dakin who make a crap product and blame a bit of carbon for making a rubbish compressor fall over. sorry peter.
    i allways use nitro ,but care is needed not to over do it as it will make pin holes that can be a pain to rectify.
    as peter says, flow over pressure.
    Dec 2009
    Spain
    229
    In Spain, many companies now are welding without N2, and then, they flush with any gas, (R22 for instance) and eliminate all the debris and carbon.
    It looks the results are quite good... maybe we'll have to make another video.
    regards,
    Nando.
    Feb 2006
    derbyshire
    610
    thats the old way, NOT ACCEPTABLE now,against the law and industry standard. why would you want to blow the crap out when you can stop it happening to start with?, plus once the pipework is carbonised theres no way of getting all of the contamination off the inner pipe surface and it will find its way arround the system and cause problems sooner or later.
    Dec 2009
    Spain
    229
    Well, I just said, companies are doing it... that's why We will have to study if it's a goo manner or not... they claim it's wonderful...
    Mar 2006
    Merate (LC) - Italy
    2,549
    This is the first time I read that nitrogen kills. Building up 74% of our atmosphere, we would all be dead by now.
    Take a full blow of nitrogen, and the worst that can happen is you getting paler and your heart beating faster for moving more oxygen around your body. It take more than a minute in pure nitrogen atmosphere for fainting.
    Nitrogen blow, again, is the old legacy, inherited and all in all obsolete way of brazing. These days, gas fluxing is the way to go. There are liquid boron compounds to be mixed with torch gas that are much more effective in reducing the black spots around brazings, and don't need you to take heavy bottles of liquid nitrogen around.
    The best of all is Fri3oil above, who flushes with R22: hope your kids don't grow with three legs or retarded...
    Dec 2009
    Spain
    229
    Quote Originally Posted by NoNickName View Post
    I must repeat I don't do that, but some of my clients. When I have children, I'll send you some pics... if they look like their mum, they'll be lovely as well.
    Regards,
    Nando.
    Oct 2003
    5,630
    Nitrogen blow, again, is the old legacy, inherited and all in all obsolete way of brazing. These days, gas fluxing is the way to go. There are liquid boron compounds to be mixed with torch gas that are much more effective in reducing the black spots around brazings, and don't need you to take heavy bottles of liquid nitrogen around....
    You can't prevent carbonizing inside the tube with adding or mixing gases to your solder flame. It's in the inside it harms the system the most.
    Only flushing with a neutral gas - not necessarily OFN - while soldering will prevents this.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Believe it or not, gasflux protects the inside of the pipe even when brazing from the outside. It probably has got some penetration capability through the swage. It worked for me so far.
    Norway
    1,043
    4
    Quote Originally Posted by Makeit go Right View Post
    THIS!
    Brazing without purging the pipe with N2 or any inert gas is just wrong
    -Cheers-
    Tycho
    Norway
    1,043
    4
    Quote Originally Posted by Fri3Oil System View Post
    regards,
    Nando.
    well that's against the law
    -Cheers-
    Tycho
    Norway
    1,043
    4
    Sorry mate, I don't care what you say or do, but no matter what gas you use, or what you mix in to the gas stream when you are brazing, it will not penetrate the overlaps on the copper pipes/fittings in any amount large enough to prevent the pipes from forming oxidation on the inside.
    and reducing black spots around brazings sure, but what about the inside of the pipe?
    -Cheers-
    Tycho
    Norway
    1,043
    4
    I'd like to see that, seriously.
    can you send me the name of what you are using, and who supplies it?
    if it works, I won't have to lug around the N2 bottle
    -Cheers-
    Tycho
    Mar 2006
    Merate (LC) - Italy
    2,549
  23. #23
    Dec 2004
    U.K
    55
    518
    HOW??
    "It probably" is hardly precise.
    Have looked at their website and it is not clear.
    Until someone could provide me with photographic and scientific evidence that it works I think I will stick with Nitrogen thanks.
  24. #24
    May 2008
    midlands
    64
    Using OFN for brazing and welding is all i know and will stick with it, leak testing the same but helium has its rewards
  25. #25
    Norway
    1,043
    4
    No way that is going to eliminate oxidation on the inside of the pipe.
    Working as a flux from the outside to make the silver/copper additive flow, and make the outside look better, sure, but preventing oxidation on the inside, nuhu, naha, not gonna happen.
    I thought it might be a powder that you dipped the end of the pipes in, and that it would create a gas when it got heated up, so it would "purge" the oxygen from the within the pipe.
    But a sole additive to the gas is'nt going to prevent oxidation inside the pipe
    -Cheers-
    Tycho
  26. #26
    Mar 2006
    Merate (LC) - Italy
    2,549
    Don't know. Works for me and that's all. Stick with OFN if you're happy with it.
  27. #27
    Sep 2003
    ISRAEL
    72
    4,248
    Any inert gas will do the job, OFN is the cheapest choice.
    When I weld SS coils, Argon is used.
  28. #28
    Jun 2009
    North East England
    712
    [quote=NoNickName;196412]This is the first time I read that nitrogen kills. Building up 74% of our atmosphere, we would all be dead by now.
    A few links to read, many people are unaware of the dangers of nitrogen when in fact it is deadly,
    http://en.wikipedia.org/wiki/Nitrogen_asphyxiation
    http://www.csb.gov/assets/document/S...en-6-11-03.pdf
    http://industrialplantsafety.com/dan...-nitrogen.html
  29. #29
    Mar 2006
    Merate (LC) - Italy
    2,549
    Again, nitrogen is not deadly, as helium is not deadly, but oxygen is necessary for breathing. One does not need any licence or authorisation to handle nitrogen.
    CO2 is toxic, nitrogen isn't.
  30. #30
    Jun 2009
    North East England
    712
    Question. if you took your gauge line and took a long deep breath of OFN what would happen.
    Answer, You would drop dead on the spot.
    Concluding that OFN is in fact deadly not toxic correct but is a suffocating gas and cannot be breathed,and causes over 8 deaths a year in the US alone
  31. #31
    Mar 2006
    Merate (LC) - Italy
    2,549
    Quote Originally Posted by james10 View Post
    No, you don't. Stop talking nonsense.
    If you breathe nitrogen, you would in theory get 20 seconds after your lungs were pretty much deoxygenated (ie, down to 30% of normal oxygen content). BUT it takes some breaths to do that, since your functional residual lung capacity (what's in your lungs at the end of a normal expiration) is 4 or 5 times your "tidal volume" (what you breathe in a normal breath). So if you take your oxygen level down (say) 20% with each breath, your oxygen is (0.8)^5 = .32 = 32% of normal after 5 breaths, so at 5 seconds a breath it takes 25 seconds to get you functionally to the top of Everest or a ****pit at 28,000 ft. Add a few more seconds for ciculation time to the head, and 40 seconds total is a fair estimate for how long to pass out. Faster, of course, if you huff and puff.
    http://yarchive.net/med/breathing_nitrogen.html
    Newsgroups: sci.chem,sci.med Subject: Re: Nitrogen KILLS Date: 7 Oct 2004 11:00:48 -0700 Message-ID: <79cf0a8.0410071000.75787115@posting.google.com>
  32. #32
    Mar 2006
    Merate (LC) - Italy
    2,549
    and c o c k pit is a perfectly legitimate word.
  33. #33
    Oct 2003
    5,630
    If inhalating helium should be deadly, then my kids and I should be death already a long time and many times when we did this when we wanted to speak like Donald Duck. You just becomes a little bit dizzy, that's all.
  34. #34
    Norway
    1,043
    4
    Here's an experiment I suggest you don't try: go into a small walk in cooler, bring with you a hose connected to a bottle of OFN, close the door, have someone on the outside open the valve on said bottle... now stay in that room for an hour...
    after an hour in there, leave the room, oh wait, you can't because you are dead...
    why are you dead? because the Nitrogen displaced all the oxygen in the room, that's why...
    -Cheers-
    Tycho
  35. #35
    Norway
    1,043
    4
    you know why you become dizzy now do you? right, right?
    obviously you dont...
    You get dizzy from asphyxia, your body is not getting the amount of oxygen you need, because you are breathing in large amounts of gas that the body cant use....
    ***** gas could be used to inflate balloons as well, they would drop to the ground tho, you could breath that gas in to alter your voice as well, it would get deeper, since it's a gas heavier than air... and you would get dizzy, because it displaces oxygen, and it is heavier than air, so it would be harder to get out of your lungs, and.
    I watched a show on TV 10-15 years ago where a ref guy used ***** to inflate an air mattress, the air mattress was in a tent, and he almost lost two of his kids because the mattress was leaking.
    Don't be stupid and inhale things people are not supposed to inhale
    -Cheers-
    Tycho
  36. #36
    May 2010
    Australia
    29
    when welding in R410A systems it is even more improtant as when the oil and refrigerant mix they form an abrasive, so with the velocity of the refrigerant pumping through your pipes it polishes the insides of your pipe work.
    So if any carbonisation is present, you will pump this through the system to be caught up in all your components.
    Can only equal disasters.
    Good practice is to always use nitro!
  37. #37
    Oct 2003
    5,630
    Yes I did Tycho - this is in fact one of the courses I give for PPL where I explain how the body reacts with changing heights and pressures and the phenomenas associating with this - but the point is that we replied to a post of James10 where he said that you will be dead with one (!!!) inhalation of OFN and this isn't true.
    You're speaking of a whole room filled with OFN and you stay in there for an hour. That's an apple/pear comparison you're making now.
  38. #38
    Mar 2006
    Merate (LC) - Italy
    2,549
    FWIW, a room filled with anything else that air would cause me to die sooner or later.
  39. #39
    Oct 2003
    5,630
    Even with pure oxygen
  40. #40
    3,853
    There was a guy i read about a few years ago, he was in an oxygen tent in hospital when he decided he needed a cigarette...
    I guess thats one way to quit smoking
  41. #41
    Feb 2009
    india
    R-22 is harmful for ozone. How they recover after flushing with R-22?
  42. #42
    Jun 2010
    glos
    71
    22
    Can you use carbon dioxide for brazing?
    If you can then hook up a pipe to someone’s mouth wile they blow down the pipe
    Reduce the end of the pipe to produce a steady flow should be able to braze the joint if they are quick before you run out of breath LOL
  43. #43
    May 2006
    Sussex
    362
    Hard to do the braze with your mounth over the end of the pipe, though.
  44. #44
    Scotland
    327
    No special flame or flux will prevent oxide formation.
    Nitrogen is not toxic.
  45. #45
    Iceberg1138's Avatar
    Iceberg1138 Guest
    I've tried CO2; it effectively stops carbon from forming in the tubing. However, CO2 can contain water where nitrogen cannot. Everyone reading this should already know that moisture is an enemy to refrigeration. So unless you want to buy medical grade anhydrous CO2 (very expensive), don't use it. I found out the hard way on this one, it took two days and triple evacuation to correct the moisture I inadvertently introduced into a ten ton split A/C system with CO2. If it were cheaper, anhydrous CO2 would be ideal. The tanks are much smaller and lighter (if you get aluminum tanks) for the same cubic feet of gas, as it is a liquid in the tank and at a much lower pressure than a full nitrogen tank is.
  46. #46
    May 2008
    Malta
    68
    67
    Nitrogen is used as it is an inert gas which means it does not react and copper when heated is reactive with oxygen.Also dry nitrogen is used for pressure testing but for brazing any inert gas will do such as co2.Nitrogen is not dangerous as long as there is sufficient air to breath so us in a well ventilated space.
  47. #47
    Aug 2001
    Leominster, MA
    71
    We use nitrogen all the time but I must admit once in a while you get that fitting that just wont close, and you chase that one joint around for an hour using up all the nitro trying to get it to close. Ive found if you get your gauge down to barely leak out and go through your manifold gauges with the hose off and connect up ffor a few minutes till it flows out an open schraeder, youll be OK but sometimes through all this when Im done it either stopped flowing or the pressure is racing. I wish the had a special set of gauges that made adjustments down to 1 or 2 PSI,... If they're out there, I haven't seen them. Nitrogen isn't harmful... you breathe it all day long...CO2 I have used in a pinch because the bottle lasts 6 times longer than Nitrogen and has much higher pressure to blow out a condenser coil of dirt. The only downfall is the bottle frosts up and looses pressure after a while till it boils off inside the bottle from resting or a handy propane torch...Nitrogen is also dry so it helps dry the system. CO2 cools the pipe a bit and this MAY cause condensation inside the piping if it were cold enough...
    My wife says I don't listen to her....or something like that....
  48. #48
    Scotland
    327
    It's possible for Nitrogen to cool larger joints if the pressure is too high, it helps to braze on a bit of capillary at the other end to keep the flow down, all you need is 1 or 2 psi but that won't be enough if you have a long run in big pipe with the end open
  49. #49
    Dec 2009
    Spain
    229
    Hi Tycho,
    I might not explained myself clearly. R-22 is not released to the ambient, it "re-circulates" and brings all the debris out the circuit, but no R-22 is released. And that is quite legal
    Regards,
    Nando.
  1. Brazing vs. soldering
    By DaBit in forum Fundamentals
    Last Post: 19-03-2011, 11:50 AM
  2. Brazing in compressors?
    By troymedhurst in forum Air Conditioning
    Last Post: 23-08-2010, 08:35 PM
  3. Flux and no flux brazing
    By SkyWalker in forum Fundamentals
    Last Post: 09-05-2010, 10:43 AM
  4. brazing rod standards
    By brian1 in forum Commercial
    Last Post: 02-05-2009, 12:00 AM
  5. Brazing Procedure Qualification
    By Delboy in forum Fundamentals
    Last Post: 18-12-2007, 07:04 AM