Results 1 to 47 of 47
-
26-11-2007, 07:09 PM #1
Need help resetting Samsung AQV12FAN
I made the mistake to turn it off for an hour (to fix an electric outlet), when I turned it on the front lights are just blinking - just like described by others in threads about other models. So I have to reset it. Does anyone have a code for it, as well as a decent how-to document?
PS: I found a how-to in another thread, but it's almost impossible to read it, it's very low resolution.
Also, can anyone confirm that the code 09 48 77 17 52 4 E works for my model?Last edited by gosheto; 26-11-2007 at 07:18 PM.
-
26-11-2007, 07:26 PM #2
Re: Need help resetting Samsung AQV12FAN
the code is:
09 48 77 17 52 45
download this how too code
http://download.yousendit.com/19260B325027FC89Paul
"KEEP IT COOL"
-
26-11-2007, 08:15 PM #3
Re: Need help resetting Samsung AQV12FAN
Thanks a lot, Paul.
This how-to is the one I complained about that it's hard to read, but in the meantime I found the SH 09 12 AWH Service Manual from another thread and it has the instructions in a easy-to-read form.
So that's not the problem anymore.
When I go thru the steps, when I plug the batteries back into the remote, the LCD's symbols flash for a second and disappear and all I see is a blank LCD. What am I doing incorrectly?
-
26-11-2007, 09:30 PM #4
Re: Need help resetting Samsung AQV12FAN
take out the batteries then holding temp up and down together put them back in,the display will read 10 00 00 then use the how to input your code or follow the sercvice manual.
the how too guide is my old one iam working on a new one in pdf formatPaul
"KEEP IT COOL"
-
05-01-2008, 02:05 PM #5
Re: Need help resetting Samsung AQV12FAN
Hello Friends,
I am new to this forum, but I have same problem with my airconditioner AQV12FAN. All lighs were flashing and isn't working.
So please Paul, becase I am new I would need one as you would say complete "how too guide", and offcource so called codes for my model.
I have had 2 times already this defect, but my air cond. is unter warranty, so I haven't eneter the "codes". Why it is so often? 2 times for 6 months.
Thanks once again Paul. Please send it to me at my mail trendafil2000@yahoo.com the code and some easy HOW TO manual.
Thanks you to all who orgainized this forums.
-
05-01-2008, 03:12 PM #6
Re: Need help resetting Samsung AQV12FAN
It's no so hard that you need a whole HOW-TO guide. Remove one battery, hold down the temp setting up AND down buttons while refitting the battery.
You should get a screen like superswill says, ie:
10
00
00
Enter the first six digits that superswill gave, then press mode. You enter the codes by pressing certain buttons for each digit/line. It's not that hard to work out which button effects what digit. Try it, and work it out, you can't go wrong if you just make sure the right digit sequence shows up when you press the mode button.
you will be greeted with another screen saying
10
00
00
Enter the next six digits that superswill gave.
press mode and the on/off
if no response you have a dead unit/receiver PCB/remote transmitterLast edited by paul_h; 05-01-2008 at 03:15 PM.
-
05-01-2008, 09:57 PM #7
Re: Need help resetting Samsung AQV12FAN
Paul, thanks a lot my dear friend.
I will try that next time when I have trouble by my self, without calling services personall. If I have problems I will ask you again.
King regards from Macedonia.
I love Australia so much!
-
08-01-2008, 08:03 PM #8
-
08-01-2008, 08:41 PM #9
Re: Need help resetting Samsung AQV12FAN
Hi,
Can someone please advise me of the code for an MH035FWEA. I have tried the codes specified in this thread, and on the PDFs from the yahoo group that is mentionned in some other threads, but not seem to fix my unit, which has E163 error message.
Thanks in advance!
Mikeyboy.
-
21-06-2008, 01:46 PM #10
Re: Need help resetting Samsung AQV12FAN
Codifica pcb MH035FWEA
0E7400-16226E
-
19-09-2009, 06:50 PM #11
Re: Need help resetting Samsung AQV12FAN
Hello SupersWill!
I have the problem with my samsung AQV12FAN. the first and third (red) light is flashing. I star the AC it has started but after short while it stops itself, and again is flashing 1 & 3 light.
I have restart with 09 48 77 17 52 45, but it doesn't help as before, when all 3 lights were flashed.
Thanks a lot,
Regards from Macedonia.
-
20-09-2009, 08:32 AM #12
Re: Need help resetting Samsung AQV12FAN
Can anyone sent me a service manual for AQV12FAN on cijevski@yahoo.com? The previos question was intended not only to the SupersWill... , sorry, it was my mistake...
-
20-09-2009, 10:40 AM #13
Re: Need help resetting Samsung AQV12FAN
Paul
"KEEP IT COOL"
-
20-09-2009, 11:16 AM #14
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Need help resetting Samsung AQV12FAN
Outdoor unit error!
Check outdoor unit LEDs display.
-
20-09-2009, 04:32 PM #15
Re: Need help resetting Samsung AQV12FAN
Thanks for your anwer. If it is outdor unit error, which doesn't have LED's display, and is not simple reset with remote, I have called techican who want large amout of money (abut 150 eur.) to change electronic, he sad maybe only onside unit electronic, maybe ouside unit electronic, maybe both. He will come in wendsday, so we will see. I wont buy samsung AC, never more.
Regards from Macedonia.
-
20-09-2009, 08:01 PM #16
Re: Need help resetting Samsung AQV12FAN
Yes you have right nike123, according to the service manual, there are LED's in outdoor unit. Thanks to SupersWill for the post. When I see which light are flasing in the outdoor unit I will inform you. Actualy, i doubt that I could do something to do about it and repair it (I am IT person) , but I will inform you. Thank to all, this forum is awesome!
-
21-09-2009, 12:03 PM #17
Re: Need help resetting Samsung AQV12FAN
Hello again,
I have seen outdor unit lights, and red BLINK, green OFF, yellow ON. OTP Error? What can I do? The AC was OFF when defect occured!!! (cose we have electricity power OFF in the building. When electricity power returned, the defect occurred.)
Regards to all,
-
21-09-2009, 09:08 PM #18
Re: Need help resetting Samsung AQV12FAN
Actually on the other shema, according to lights on outdoor unit (red BLINK, green OFF, yellow ON), is written "Option Error (EEPROM)".. What shuold I do?
Regards...
-
22-09-2009, 07:29 AM #19
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Need help resetting Samsung AQV12FAN
................................
Last edited by nike123; 22-09-2009 at 08:30 AM. Reason: wrong diagnosis
-
22-09-2009, 09:27 PM #20
Re: Need help resetting Samsung AQV12FAN
enter the option code once then ring a local technition,the option code is very often used as a magic wand fix but it is only a way of telling the indoor PCB what model and capacity it is operating in, and offers no more of a reset than turning the system off and on with the local remote
Paul
"KEEP IT COOL"
-
22-09-2009, 09:41 PM #21
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Need help resetting Samsung AQV12FAN
I have conversation with OP and it is probably outdoor unit EEPROM error (from frequent power outage), since option code reset doesn't help at all.
Is it possible that outdoor EEPROM is lost its data and cannot communicate with indoor unit and therefore such error?
Does Samsung have any tool to reprogram that EEPROM?
-
23-09-2009, 08:01 PM #22
Re: Need help resetting Samsung AQV12FAN
Paul
"KEEP IT COOL"
-
28-09-2009, 01:21 PM #23
Re: Need help resetting Samsung AQV12FAN
I agree with you nike123, algtough I am not mechanic person. But I have "frequent power outage". The AC wasn't working when defect occured. When the same defecet occured on the indoor unit (indoor EEPROM) because "frequent power outage" I solved that with entering the codes.
I guess I couldn't do a lot in this case...
Regards to all,
-
28-09-2009, 01:29 PM #24
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Need help resetting Samsung AQV12FAN
You could only complain to Samsung for constructing such stupid system.
No other manufacturer have this type of problem.
Toshiba (and some other high class manufacturers) also have universal outdoor unit for more than one indoor unit (production cost cutting) but it does no require codes. It is achieved simply by jumpers on PCB.
-
02-10-2009, 09:50 AM #25
Re: Need help resetting Samsung AQV12FAN
Does no one knows to give me advice?
EEPROM outor unit error, acording to oudor flashes. The AC wasn't working when defect occured. The indor has 1 & 3 light blinking (outodor unit error).
Regards,
-
04-10-2009, 12:16 PM #26
Re: Need help resetting Samsung AQV12FAN
Hello my friends,
SAMSUNG AQV 12 FAN.
I would ask SupersWill, and others, to provide for me the content of OUT DOOR unit, EEPROM. (IC 93LC56 on the service manual). I need that file to over write outdoor unit EEPROM. It would be best if someone could provide me both content, of indoor and out door unit EEPROMS. That supose to be a files.
Could someone, sSupersWill, or other provide such file(s)???
Regards from Macedonia...
-
30-11-2009, 08:41 PM #27
Re: Need help resetting Samsung AQV12FAN
Hello all,
Can anyone help me with what this error means? I have just replaced the indoor PCB on a SC24TA8/XSA after Gekkos had a party in there. Now all the front indicators are flashing. Am I right in understanding that the unit needs resetting?
Please help
-
05-01-2010, 08:58 AM #28
Re: Need help resetting Samsung AQV12FAN
i have the same problem with the lights 1 and 3 blinking.
i set up the code than turn on the device. it works on cold mode but when i set the sun it stops, the outdoor unit work few minutes than stop and lights start blinking again . Any ideas?
-
05-01-2010, 09:10 AM #29
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
05-01-2010, 10:51 AM #30
Re: Need help resetting Samsung AQV12FAN
operation & turbo
-
05-01-2010, 11:44 AM #31
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
05-01-2010, 02:05 PM #32
Re: Need help resetting Samsung AQV12FAN
look man , every time when this problem comes i call to some service technician , and he make the same steps like me than the unit is working. I think that he use some different code
-
05-01-2010, 04:08 PM #33
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Need help resetting Samsung AQV12FAN
Sorry man, I cant help you if you are not cooperative!
-
12-04-2010, 07:48 PM #34
Re: Need help resetting Samsung AQV12FAN
Hi , I need help for AC AQV12FAN , after I pluged in power outlet AC make self test , and then start itself to cooling then heating then switched off then start again and agin .
-
13-04-2010, 02:35 PM #35
Re: Need help resetting Samsung AQV12FAN
Try option code 09 48 77 17 42 4 E
-
24-04-2010, 05:37 PM #36
Re: Need help resetting Samsung AQV12FAN
Hello friends,
I am little bit confused about option codes. Now we have advice from SeeU for option code 09 48 77 17 42 4 E. At the beggining of this page there is 09 48 77 17 52 45 code posted from SupersWill. Could someone cofirm to mee wich code is right? Or send me a code to cijevski@yahoo.com. Or different problems need diferent codes for same model Samsung AQV 12 FAN. In the option codes.pdf we have 09 48 77 17 52 4E. Tree diferent codes. Which is right code one?
-
08-05-2010, 04:40 PM #37
Re: Need help resetting Samsung AQV12FAN
Any answer friends?
SupersWill, anyone?
-
25-05-2010, 12:31 PM #38
Re: Need help resetting Samsung AQV12FAN
Still no answer from anyone.......
Nor mail... nothing....
The question was...
"Hello friends,
I am little bit confused about option codes. Now we have advice from SeeU for option code 09 48 77 17 42 4 E. At the beggining of this page there is 09 48 77 17 52 45 code posted from SupersWill. Could someone cofirm to mee wich code is right? Or send me a code to cijevski@yahoo.com. Or different problems need diferent codes for same model Samsung AQV 12 FAN. In the Option_Codes.pdf we have 09 48 77 17 52 4E. Tree diferent codes. Which is right code one?"
-
26-05-2010, 06:58 AM #39
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
26-05-2010, 08:49 AM #40
Re: Need help resetting Samsung AQV12FAN
Ok from the service manual the original option code for the AQV12FAN is;
09 48 77 17 52 4E
A later bulletin recommends using
09 48 77 17 42 4E
this appears to disable the auto-restart function which should help the indoor unit retain the option codes in the event of power failure.
To be honest I don't understand how this actually works.
Code 09 48 77 17 52 45 does not appear to exist, so I cannot recommend using it, however my information is a bit limited.
Hope thi shelps
Regards
Loops
-
26-05-2010, 10:32 AM #41
Re: Need help resetting Samsung AQV12FAN
Thanks a lot.....
That is a kind of explanation i needed for.
If anyone disagree, please do write.
King regards....Last edited by cijevski; 30-05-2010 at 11:29 AM.
-
03-06-2010, 12:19 PM #42
Samsung sh12zwhd
Can anyone help me with my Samsung SH12ZWHD? All three lights are blinking.
Thanks a lot!
-
04-06-2010, 12:40 PM #43
Re: Samsung sh12zwhd
Based on my humble and very modest experience with my Samsung AQV 12 FAN, I think that you need code for resetting it. I don’t have it. There is a file on following link http://www.refrigeration-engineer.co...t=option+codes. There should be a code for your model. Is it the right one? That question I was asking myself for my model, as you can see, and here above are answers that I had. And still have a doubt which I right one J.
For my model code in the book is 09 48 77 17 52 4E. Sugestion from SupersWill, on this thread, which does work for me is 09 48 77 17 52 45. Maybe the code from book would work. I haven't tried it.
So I really couldn't help you about finding the right code, and what some code does the AC, if there are more.
If you find it how to reset it? It is described above in this thread by SupersWill.
Thanks for all who do participate in this thread.. King regards and all the best….Last edited by cijevski; 04-06-2010 at 09:33 PM.
-
05-06-2010, 03:06 PM #44
Re: Need help resetting Samsung AQV12FAN
Cijevski, thank you so much!
I entered the code and it seems that everything is okay.
Why did the problem occure do you know maybe?
Anyway, thank you, and thank all of you that are helping each other on this forum!
-
07-06-2010, 02:04 PM #45
Re: Need help resetting Samsung AQV12FAN
Dear Friend,
I am happy that you have solved your problem.
Because I am not mechanic, I am just regular guy who had similar experience and wait mechanic to come 2 weeks for same kind of problem and pay for this. Which code does work for you, I am interested, from book Option Codes? You should thank not to me but to SupersWill and others who keep alive this forum and this thread…….
Why this happen? Based on that I have read until now, it is because unstable electricity supply.
Best wishes my friend,
Cijevski,Last edited by cijevski; 07-06-2010 at 02:10 PM.
-
08-06-2010, 07:20 AM #46
Re: Need help resetting Samsung AQV12FAN
This was my code - 2502570340, the only one for Samsung sh12zwh.
Kind regards
-
15-06-2010, 04:35 PM #47
Re: Need help resetting Samsung AQV12FAN
You can just replace the filament.
Thanks camsltd
Similar Threads
-
Samsung RS21 DCNS Fridge too warm
By Divekate in forum Trouble ShootingReplies: 1Last Post: 26-02-2007, 05:12 PM