09-05-2010, 06:26 AM #1
YORK YAEP HIGH DESCH ERROR...PLS Help
Hi,
i am facing problem that now a days in summer, at around 12-1 when the ambient temperature rise to around 40-43'C the chiller stops, and gives error of High desch.
we checked the filter drier cores, gas , solenoid ,exv etc....everything seems to be normal & at around 3-4 pm when there is slight decrease in temperature the machines become good & keep o workinng.
kindly advice what needs to be checked or done.
the chiller is YAEP YORK.
the chiller works for max 5 minutes & then stops.
do i need to increase the programed data & if yes thenn i dont have code to edit that.
kindly guide me as i may loose my job because of this problem.
thanks
-
09-05-2010, 09:26 AM #2
Re: YORK YAEP HIGH DESCH ERROR...PLS Help
Well...the problem is soved through this forum as i found that the Discharge pressure cutout was set low by our rival contractor who handedover these chillers to us changed the discharge cutout settings.
thanks any ways.
-
09-05-2010, 09:27 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: YORK YAEP HIGH DESCH ERROR...PLS Help
Check fan rotation.
Clean condenser (wash).
Measure condensation pressure, air in and out temperature and post what is HP alarm setting set on unit. You could do that when temperature is not that high, but few °C lower (before alarm is expected to occure).
-
09-05-2010, 10:12 AM #4
Re: YORK YAEP HIGH DESCH ERROR...PLS Help
thanks for the guidance. my problem is already solved....through the Code 7396...as i increased the high pressure cutout.
-
09-05-2010, 10:49 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: YORK YAEP HIGH DESCH ERROR...PLS Help
Are you sure that you did not exceeded compressor operating limits and that someone has changed that value before?
If commissioning engineer done that, you may also expect some other sabotage.
Few times, contractors I worked for, asked of me to do the simmilar, but I refused.
-
09-05-2010, 05:36 PM #6
-
09-05-2010, 09:29 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
15-06-2010, 06:39 PM #8
Re: YORK YAEP HIGH DESCH ERROR...PLS Help
If u know who did that and sabotage the unit u should report that to local authorities and to Johnson Controls,because such actions damaging the name of the refrigerator engineers and the companies working for,and of course they engineer that carried out that sabotage is totally a moran
Similar Threads
-
YORK YAEP recip chiller fault
By chiller1 in forum Trouble ShootingReplies: 8Last Post: 04-06-2010, 10:41 AM -
Over charged system... what symptoms?
By Clk320_Greg in forum Trouble ShootingReplies: 2Last Post: 19-10-2009, 06:25 PM -
York Chiller High Line Voltage Problem
By shamyl in forum ElectricalReplies: 5Last Post: 19-07-2009, 07:53 PM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM