29-04-2010, 11:38 AM #1
Effect of oversized condenser?
Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????
Q no 2) Secondly what will be the effect if a 2Ton compressor is used in a Ton system??
-
29-04-2010, 05:29 PM #2
Re: Effect of oversized condenser?
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
04-05-2010, 01:47 PM #3
Re: Effect of oversized condenser?
oky thanks
-
04-05-2010, 02:36 PM #4
Re: Effect of oversized condenser?
Originally Posted by mianrizwan :
Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????Goshen :
low head pressure ,system will work unstable
Where does the instability come from? Are you thinking on terms of driving pressure-difference across the orifice & possible hunting?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
04-05-2010, 09:06 PM #5
Re: Effect of oversized condenser?
The system will be overcondensing resulting in an unstable supply of liquid at the tev inlet.
Low head pressure without a c/fan spped controller can contribute to low pressure trips certainly on cold days.
A 2 ton compressor on a 1 ton system will result in very high discharge pressure and overheating of the compressor providing it doesnt trip the HP safety first.
Are these theoretical questions or are you building a system like this?
-
04-05-2010, 09:35 PM #6
Re: Effect of oversized condenser?
i hope not,!!
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
Similar Threads
-
Parallel condensers Shell and tube paralle with Evaporative Condenser
By Herschmidt in forum NH3Replies: 2Last Post: 08-06-2010, 11:12 PM -
Condenser Temperature. HOW TO model it in 3D?
By ruzfactor in forum FundamentalsReplies: 6Last Post: 07-09-2009, 10:57 AM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM