27-04-2010, 12:10 PM #1
Taylor 754
I need to change oil in compressor. Is there anyway to find correct amount of oil. It is one of the large r-502 compressor. Part # is 048259 Taylor parts list Bristol as compressor brand.
-
27-04-2010, 04:25 PM #2
Re: Taylor 754
hi jim, you need to reclaim the gas, possibly disconect the compressor pour out the oil into a container messure the amount of oil you have taken as an indicationof how much oil is requiered, check with the wholesaler the correct type of oil and the amount requiered < and seal the fridge system whilst you are ready to carry on the job< reconnect the compressor, fit new dryer, pressure test with ofn, whilst vaccing out, suck the oil in, weigh in new gas, run on test, leak test, ok
just a question ? why do you want to change the oil?Last edited by sedgy; 27-04-2010 at 04:29 PM. Reason: terrible spelling 1-10
-
28-04-2010, 06:44 AM #3
Re: Taylor 754
System has had leak repair and am changing from R502 to R404. Have new dryer to replace after I flush system and change oil.
-
28-04-2010, 11:49 AM #4
Re: Taylor 754
ok jim , all the best with the job,
I was just being nosy, about you changing the oil -sedgy .
-
28-04-2010, 12:21 PM #5
Re: Taylor 754
Hi jimsfaust,
Have new dryer to replace after I flush system
Just interested.Tony
-
28-04-2010, 12:38 PM #6
Re: Taylor 754
I also wanted to know how did you flush the system... have you cleaned it or just flushed?
-
28-04-2010, 03:46 PM #7
Re: Taylor 754
R11x flush
-
28-04-2010, 04:07 PM #8
Re: Taylor 754
Isn't it forbidden in the US? Here it is... here companies clean the circuits properly, without releasing any gas to the atmosphere
-
28-04-2010, 08:27 PM #9
Re: Taylor 754
R11x is a solvent not a refrigerant. It is not R11
-
29-04-2010, 08:08 AM #10
Re: Taylor 754
Ok, I got it now, didnt read the "x"... Anyway, if you used a solvent, you may still have some of that solvent on that circuit. It's better to use the same refrigerant of the installation in order to extract all acids, oils, water, or whatever.
With this method, you can recycle the refrigerant you are using on site, and reuse it afterwards- (not in this case that your are retrofitting the plant, of course)