    EKC 315A Strange Problem



    Hi,

    At work last night I faced a very strange problem, all the sudden ... 7 numbers of EKC 315A controllers stopped working properly.... They were all showing temperatures of 140C and above!!!! I connected on of them with a probe, and it was sensing temperature but as if it were adding 120C to the actual value!!!


    I am really clue less.. how can this happen, 7 numbers of EKC 315A at the same time!! and showing the same problem..

    I tried to reset one controller to original factory setting, and then loading the parameter, but still the same issue... Kindly help me A.S.A.P if anyone had the same issue before.

    and thanks in advance.



  2. #2
    Join Date
    Jan 2009
    Location
    UK
    Age
    58
    Posts
    161
    Rep Power
    16

    Re: EKC 315A Strange Problem

    Hi quark555,
    Are these controllers connected to a network, if so what is the front end?
    One explanation would be a network error that has sent bad information to these controllers and caused the issue you have found.

  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: EKC 315A Strange Problem

    Hi

    Several scenarios can exist!

    Do you have PT 1000 sensors on it?
    Did you connect the probe straight on the controller when testing?
    Did somebody cut probe cables by accident?
    What is the r05 parameter set to?
    What is the o30 parameter set to? Did it match the Refrigerant in use?
    What is the 017 parameter set to? Temperature? Superheat? Valve opening degree?

    Normally when probe wires are open circuit, they show high readings.

    Come back on this matter if possible.
    I am not always right, but I'm never wrong!

  4. #4
    Join Date
    Apr 2010
    Location
    UAE
    Posts
    12
    Rep Power
    0

    Re: EKC 315A Strange Problem

    Dear Silhouette,
    Yes they are connected through LanBus network. But I already isolated the controller, restarted it, and same result. (I don't know if restarting it should help). Suppose that it was network problem, how to resolve it? even though thel Lon Network is workig fine since that we are actually getting alaram normally and we can view all the different nodes.
    And thanks you in advance.

  5. #5
    Join Date
    Apr 2010
    Location
    UAE
    Posts
    12
    Rep Power
    0

    Re: EKC 315A Strange Problem

    Dear Eeram,

    Below my answers in blue.

    Do you have PT 1000 sensors on it?
    Yes PT 1000

    Did you connect the probe straight on the controller when testing?
    Yes I connected the probe straight on the controller while testing.

    Did somebody cut probe cables by accident?
    No. (Actually I imagained that all the cables were going in one cable try a something happened over there.. but i


    What is the r05 parameter set to?
    C-b



    What is the o30 parameter set to?
    19

    Did it match the Refrigerant in use?
    Yes it's matching the refrigerant in use.

    What is the 017 parameter set to?
    01
    Temperature?
    Superheat?
    Valve opening degree?

    Normally when probe wires are open circuit, they show high readings.
    (I used brand new probe while testing, and I checked its resistivity, and it was fine and normal)

    And thank you for your help.

  6. #6
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: EKC 315A Strange Problem

    sounds like a power surge, i have had similar problem a few times when the building was hit by lightning, this was on elm controllers though,we had to replace about 20 controllers in 1 go.

  7. #7
    Join Date
    Apr 2010
    Location
    UAE
    Posts
    12
    Rep Power
    0

    Re: EKC 315A Strange Problem

    Thank you coolhibby for your reply. Actually I suspected that.. but unfortunately our BMS didn't register any power interruption. Thus we couldn't prove it for our management.

  8. #8
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: EKC 315A Strange Problem

    hi quark this will be because the the bms system will have more than adequate surpression,a lanbus network nor the 315 controllers have any surpression!

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. Hitachi RAS-20FSG strange problem with fuse
    By ewgeny in forum Air Conditioning
    Replies: 2
    Last Post: 08-03-2010, 09:26 AM
  3. YORK YCAM B450 strange PCB problem
    By exxu in forum Trouble Shooting
    Replies: 6
    Last Post: 17-02-2009, 01:17 PM
  4. Strange compressor problem
    By Spoc in forum Trouble Shooting
    Replies: 15
    Last Post: 09-10-2007, 05:04 PM
  5. strange inverter problem
    By rbartlett in forum Air Conditioning
    Replies: 11
    Last Post: 19-05-2006, 08:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •