    Walk in cooler running 48degrees



    I am working on walk in cooler and it is running no colder than 48 degrees . The suction pressure is at 30psi and the hi side is at 210. I charged the unit propery and everything is working correctly. Anybody have any suggestions on how to get this thing below 40 degrees



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk in cooler running 48degrees

    Obviously, everything is not working correctly... and pressures don't mean a thing if we don't know what refrigerant is in the system.

  3. #3
    Join Date
    Mar 2010
    Location
    usa
    Posts
    8
    Rep Power
    0

    Re: Walk in cooler running 48degrees

    R404A is in the system

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk in cooler running 48degrees

    What does "charged the unit properly" mean?

  5. #5
    DRAGA MICHAEL's Avatar
    DRAGA MICHAEL Guest

    Re: Walk in cooler running 48degrees

    Hello comrad ,i had such senerio one time too,the reason is all about refrigeration load and refrigeration system capacity balancing.
    for further clarity on how to go about,i shall request you to send dimensions of your walk in cooler and category, expected load,ambient conditions and final temperature you need to achieve.

  6. #6
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: Walk in cooler running 48degrees

    hello there not wishing to seem rude but have you got the pipes the correct way round ? not using the evap as the condenser an vice versa and did you install it and did you follow the instructions to the letter

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Walk in cooler running 48degrees

    I would suggest getting a refrigeration engineer involved.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: Walk in cooler running 48degrees

    what is the air temperature going over the condensr[ambient] is the condensor clean.

  9. #9
    Join Date
    Mar 2010
    Location
    Australia
    Posts
    7
    Rep Power
    0

    Re: Walk in cooler running 48degrees

    Start with the gas charge mate. Your pressures seem a bit low. How have you charged the system "properly"?

  10. #10
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: Walk in cooler running 48degrees

    the timer stucks on defrost and the indoor fan is working, therefore mag valve is shut i. e constant back pressure.
    switch off the unit , open controll box, turn on unit check for the s/c on timer.
    good luck.

  11. #11
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: Walk in cooler running 48degrees

    for charging gauge it up to high side,get your comparator check ambient temp add 15c on top, you must see exactly same psig as your calculation???????????
    do you!

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Walk in cooler running 48degrees

    Hopefully you liquid charge system into the high side.
    Vapour charging will give the exact problem you have described, on R404A.
    magoo

Similar Threads

  1. Design td on walk in cooler
    By IMSTIEN in forum Technical Discussions
    Replies: 2
    Last Post: 01-10-2009, 10:18 PM
  2. Replies: 3
    Last Post: 02-07-2009, 04:47 PM
  3. Walkin cooler running to warm need help
    By The Butcher in forum Trouble Shooting
    Replies: 7
    Last Post: 03-08-2007, 09:19 PM
  4. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM
  5. Walk in Cooler (short cycling)
    By Brandon in forum Trouble Shooting
    Replies: 11
    Last Post: 05-05-2003, 11:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •