14-04-2010, 09:40 AM #1
air source heat pump:how to make water reach 80℃?
In air source heat pump system, how to make water temperature reach 80℃? Only choose different refrigerant and compressor ? How to evaluate COP, does it relative to rated hot water output volume? For example:
heating capacity: 34.5KW(120000btu)
COP:2.7
Rate hot water output volume: 560Liter/hour
rated power input: 12.8kw
rated current input: 25.2A
max power input: 17.3kw
max current input:34.1a
scroll compresor, R134a,
How about the COP:2.7, how about the rated hot water output volume:560l/h.low or high?
Thanks for your kindly suggestion.Have a good day.
-
14-04-2010, 09:43 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: air source heat pump:how to make water reach 80℃?
Easy. Fit desuperheater before condenser!
Last edited by nike123; 15-04-2010 at 12:20 AM. Reason: Just that someone doesnt realy think that is just that easy.
-
14-04-2010, 10:15 AM #3
Re: air source heat pump:how to make water reach 80℃?
As easy as that, "I wish"
You can but what ever set of numbers you want into a program and get the answers you want. So that being the case yes numbers looks OK.
-
14-04-2010, 10:22 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
14-04-2010, 12:19 PM #5
Re: air source heat pump:how to make water reach 80℃?
Have fun on the condenser 'pinch'.
Will be useful to have a few spare compressors on hand.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
14-04-2010, 07:45 PM #6
-
14-04-2010, 10:25 PM #7
Re: air source heat pump:how to make water reach 80℃?
Is it really so easy?
Surely you need to consider the gas characteristics?
You need to look at a Ph diagram and see there are different dicharge temps for each and every refrigerant. A superheater wont give you the 80C you need if the refrigerant can't deliver the temperature at the desired pressure..... so is this still "simple"Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
14-04-2010, 10:35 PM #8
Re: air source heat pump:how to make water reach 80℃?
-
14-04-2010, 11:02 PM #9
Re: air source heat pump:how to make water reach 80℃?
For a start forget about R134a. Look at R22 (but that's being phased out) so check out CO2. Look for a compressor with 2 stage compound, I saw a rotary as such yesturday but a scroll would be better. Operate in the transcritical region and be careful of the pinch like mad fridgie said.
As for the COP measure it = output (heat added to water) divided by input (kWs electrical power)
-
14-04-2010, 11:13 PM #10
Re: air source heat pump:how to make water reach 80℃?
I think scrolls have a condensing limit with R134A about 70C / 21barg discharge temp ~ 82C will this be enough? ... will a scroll run happily at this limit and will it's service life be compromised?
... is this still "simple"Last edited by nevgee; 14-04-2010 at 11:15 PM. Reason: duplication
Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
14-04-2010, 11:33 PM #11
Re: air source heat pump:how to make water reach 80℃?
As a manufacture of heat pumps who produce water just short of 90C with eCOPs of upto 10, I can say in theory it is that easy!, in practice is certainly not. At these temps very small changes can make very big. differences in performance and reliabilty.
there are number of methods of achieving these temps, I personally think CO2 heat pumps are overrated at its current price tag.
-
15-04-2010, 12:59 AM #12
Re: air source heat pump:how to make water reach 80℃?
First,thanks for all the comments and suggestions above. You're welcome to continue ......
sorry, the inlet water temperature is 27℃, ambient tem(dry ball/wet ball)7℃/6℃. Inlet and outlet water tem in condenser: 40℃/60℃, the max tep. can reach 80℃. How about the inlet and outlet water tem. in condenser? How about the COP:2.7, how about the rated hot water output volume:560l/h.low or high?
Thanks for your kindly suggestion.Have a good day.
-
15-04-2010, 01:44 AM #13
-
15-04-2010, 02:51 AM #14
-
15-04-2010, 03:48 AM #15
Re: air source heat pump:how to make water reach 80℃?
^ Why don't you hire MF to design your next range of heat-pumps?
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
15-04-2010, 04:01 AM #16
-
15-04-2010, 04:29 AM #17
Re: air source heat pump:how to make water reach 80℃?
Thanks DesA, It would be nice to have a fully paid trip to China!
Billiu2010, you are sort of correct this forum is free exchange of ideas, but not when it come to interlectual property.
Your first questions were acceptable and we have given answers.
When it comes to how to, you need to research, test, blow-up equipment, gain experience and basically spend a lot of money.
If you want to use the forum to full potential, you need to ask very specific questions, then you can get the answers from indvidual specialists.
If you developing in this market, then you will be poor, just like the rest of usLast edited by mad fridgie; 15-04-2010 at 04:31 AM.
-
15-04-2010, 05:07 AM #18
-
15-04-2010, 05:34 AM #19
Re: air source heat pump:how to make water reach 80℃?
Generally people who want a free exchange bring nothing to the table.
-
15-04-2010, 07:38 AM #20
Re: air source heat pump:how to make water reach 80℃?
Thanks for all the comments related with this suject . I agree with your opinions. If my question come to interlectual property, I would like to exchange for the evalue it cost. Of course i would like to invite MF to china if he can help me with IP issues.
But my question is ask how about the evalue of cop and outlet water volume , inlet and outlet water tem from condensor, do these related with IP . I'm puzzled..........
-
15-04-2010, 07:48 AM #21
Re: air source heat pump:how to make water reach 80℃?
(L/S * 4.187 * (To-Ti))= Heat output
KWout/KWin = COP
No Not IP
Done!
-
15-04-2010, 10:45 AM #22
Re: air source heat pump:how to make water reach 80℃?
No IP to China, sorry.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
15-04-2010, 01:57 PM #23
-
15-04-2010, 02:44 PM #24
Re: air source heat pump:how to make water reach 80℃?
Hi billliu2010
Not sure where you got your numbers from. On a quick calc (roughly) from water 20K and flow of 0.155l/s I get 13kW. If you measure A and V then multiply A, V and power factor you will have you power input in kW's. So divide the output kW's by input kW's.
For the flow rate 560l/h is the same for a shower. You can search this forum for all the data you need such as COP, formulas, caclulations and other technical matters.
-
15-04-2010, 03:54 PM #25
Re: air source heat pump:how to make water reach 80℃?
It would perhaps be a start if you placed some of your ideas, proposals, calculations, sketches, or solutions up on the board for us to comment on.
This will be both useful for you as well as for the forum members. In this way, we all get to learn something new. Then it becomes a win-win situation instead of members giving you solutions on a plate.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
15-04-2010, 06:43 PM #26
Re: air source heat pump:how to make water reach 80℃?
The rating is for a starting temperature of 27 C. Running the numbers
one liter of water weighs 1 kg
Q = kg/hr*cp*∆T
cp = 1 cal/gm/˚C or 1000 cal/kg/˚C
Q = 560*1000*(80-27)=29660000 cal/hr
Q = 34.5 KW
So if your entering water is cooler than 27 C, or if the heat pump condenser air is cooler than design, you will not get 80 C water out.Last edited by dougheret0; 15-04-2010 at 06:46 PM.
-
15-04-2010, 07:31 PM #27
Re: air source heat pump:how to make water reach 80℃?
I still hold the conclusion that with ambient temp of 6 or 7 degrees C you are better off "preheating" the water with the heat pump and then using Gas or electric fired Boiler to finish the Job.
-Christopher
-
16-04-2010, 03:26 AM #28
Re: air source heat pump:how to make water reach 80℃?
Yes, it's my start here and it's the good atmosphere here that let me decide to be a member ,without my info. where is the hot discuss, where is something new , not a win-win? Don't so be practical.
Then, what's the meaning of " No IP to China",does it
relative with my question? pls kindly suggest,thanks.
-
16-04-2010, 03:36 AM #29
Re: air source heat pump:how to make water reach 80℃?
It's very simple. What I've noticed during my time on RE, is that a number of probing questions seem to come from China, but very little, if any, information flows back to the forum for others to digest. It seems like a one-way flow. This is basically unfair.
My personal view is not to send any IP to China. You will find that this view is also shared by a number of developers. There are numerous stories of blatant IP theft in China, & I have no interest in making you, or your company wealthy off free IP. If you are prepared to pay the going market rate, then I'm sure that some parties will be prepared to discuss with you.
Anyway, apologies for interrupting your thread with my personal view. Put up your calculations & I'm sure you will get some interesting answers.Last edited by desA; 16-04-2010 at 03:39 AM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
16-04-2010, 03:45 AM #30
Re: air source heat pump:how to make water reach 80℃?
Can make it with the above mentioned data after confirming with our related engineer.....
As for CO2 heat pump can make it also and it's mature in Japan, and then in Europe,but it's cann't be popular at present because of it's high price. Just like what you said.Thanks!
-
16-04-2010, 04:05 AM #31
-
16-04-2010, 04:26 AM #32
-
16-04-2010, 04:56 AM #33
Re: air source heat pump:how to make water reach 80℃?
As for one-way flow, I has the same idea as you, I cann't stop others from doing this,but I'm trying not to .
As for the IP issue, I don't want to comment much, I only say" part doesn't stand for all" , If you insist on your prejudice ,this forum will lose something in a certain degree. We are for technical free discussion (excluding IP)but not politics, we should always try to find good things and try to prevent bad things without any prejudice. This is my private opinion .
Anyway,thanks for your time of telling me why. No need apologies because we should have a free and friendly atmosphere here.
Thanks for all the friends comment here.
-
16-04-2010, 05:18 AM #34
Re: air source heat pump:how to make water reach 80℃?
DesA and Mad fridge, stand up and take a bow.
magoo.
-
17-04-2010, 02:26 AM #35
-
17-04-2010, 04:52 AM #36
Re: air source heat pump:how to make water reach 80℃?
Amazed at how the OP moves from being a poor individual interested in heat-pumps, to one with customers and engineers.
If you want IP, arrange a technology transfer deal for your company, & pay for it. Someone may want to assist you, but certainly not me.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
17-04-2010, 10:10 AM #37
Re: air source heat pump:how to make water reach 80℃?
Hi billliu2010
Yes 8 - 10 l/s is what is used in ausie and nz.
No disrespect to other members but in my mind patents and IP are not really fair, in saying that I would be pissed if someone else patented one of my ideas and I do realise that some need to make a living and invest on R+D, requiring a return. Considering some inventors have been knocked off for thier ideas.
Search my threads and I'm sure you will find most if not all the info you need.
-
17-04-2010, 04:53 PM #38
Re: air source heat pump:how to make water reach 80℃?
Historically, almost all inventors are knocked off for thier ideas. Patents are at best ineffective and at worst counter-productive. When you apply for the patent, you tell the world how you did it.
There is no effective way to reward the people who most benefit mankind. Its a wonder that technology keeps moving forward. The only real protection is secrecy... and you will need to reveal those secrets to those who develop/build/market your ideas. Who can you trust?
When you build the better mousetrap, the IP thieves beat a path to your door.Last edited by Gary; 17-04-2010 at 06:41 PM.
-
18-04-2010, 01:06 AM #39
Re: air source heat pump:how to make water reach 80℃?
Patents are useful in countries where the IP can be strictly enforced.
IP thieves will always be what they are - thieves. This is why very few developed nations will send new technology to Asia.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
19-04-2010, 02:46 AM #40
Re: air source heat pump:how to make water reach 80℃?
-
19-04-2010, 03:10 AM #41
Re: air source heat pump:how to make water reach 80℃?
Develop your own IP at cost, then you too can protect it.
As Tesla stated, do a search on RE, there will be a lot of information (the free sort) to help you on your way.
As I also stated, do take care of the 'condenser pinch'. Pushing temp over 80'C is possible & some of us have developed technology to do exactly this, and higher actually. We will however, protect that knowhow, in order for our families to eat.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
19-04-2010, 03:15 AM #42
Re: air source heat pump:how to make water reach 80℃?
If my quetion is related with IP wittingly or unwittingly,I won't force you to answer, I cann't,you can choose not to answer, if you are enough friendly ,you can tell me my question is related with IP.
I have said if I need IP,I will pay for it ,of course not you. NOT always exagerate such simple questions, pls kindly confirm what is IP, what isn't IP, not to say everything is IP,or you cann't speak here.
My word is not only to you, to all the persons who always want to exagerate something or with discrimination.
Here should be a place to discuss things about heat pump freely and friendly, not alway to talk so much nonsense things,or what's the meaning of establishing this forum?
Thanks for all the comments on this issue!!
-
19-04-2010, 03:34 AM #43
Re: air source heat pump:how to make water reach 80℃?
Hi billliu2010,
If you & your company is serious about purchasing IP, which you now seem to be, then MF has made you an offer to assist. Talk with him, using the private-mail feature on the RE board. He's a nice guy & will get you sorted out, I'm sure.
All the best & apologies for being a little hard on you.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
19-04-2010, 02:37 PM #44
Re: air source heat pump:how to make water reach 80℃?
in a design phase if something is regarded as a design secret or IP.. why even post about it on an open forum?
I work on and design a lot of things.. some of the projects are fun, some are proof of concept, some are truly design.. I only post on an open internet forum those projects and ideas which i feel may be helpful to others without compromising my possible future business ventures....
sure, like anyone else I enjoy and like to entertain others' ideas, however I dont Expect just because I post here that someone is going to come along and do the job for me for free.... so I expect on a forum vague ideas and responses... often those point me in a direction that is a huge help..
-Christopher
-
20-04-2010, 02:53 AM #45
Re: air source heat pump:how to make water reach 80℃?
different jobs ,different requirement, different opinions! I'm sales ,only concept, no IP needed, so pls don't worry, I won't seize your bowl.
-
20-04-2010, 04:05 AM #46
Re: air source heat pump:how to make water reach 80℃?
The story-line morphs yet again.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
20-04-2010, 06:01 AM #47
Re: air source heat pump:how to make water reach 80℃?
I thought I would clear up the IP
The vapour compression refrigeration cycle has been around over 100 years, it has been tweeked, different compressor, elctronics, refrigerants, but all said and done it has not changed, you can not beat the laws of physics.
So you need six parts, compressor, evap, cond, expansion device, refrigerant and some thing to drive the system. Understand this then you are on your way.
IP or could be said Knowledge, this is gained through experience, some information we share, other information we do not. The NOT information is normally info that may effect our businesses, thus our families. Of course this information can always be purchased, this is the case when ever you pay for something that you can not do yourself.
In this field it is normally the concept/application that is classed as IP more than specifics, very few of use can say that we have built a whole system from raw materials (I have not), most still requirer major components from others, example compressor (only a limited number of manufactures world wide)
-
20-04-2010, 06:16 AM #48
Re: air source heat pump:how to make water reach 80℃?
IP, or specialised knowhow.
Every professional uses their specialised knowhow to earn a living - lawyers, doctors etc. Engineers are no different.
Raising water temp reliably & safely to 80'C does require a certain amount of specialised knowhow - this knowhow comes at a cost in terms of design, experimentation & analysis expenses. The specialist engineer has a right to both protect this knowhow, & to charge for it, in order to recover their financial outlay.
What many specialists do, however, is to combined their specific expertise into co-operative ventures, where information is inter-traded, until a certain final product is ready for market release. The profits from these products are then shared amongst the co-operative partners.
Much of the information on RE is of a very general nature & can be freely shared. The ethical questions arise when specialist information is requested. If certain members are prepared to provide this information at no cost, then that is their right. We all have different views on where we draw the line.Last edited by desA; 20-04-2010 at 06:21 AM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
22-04-2010, 09:22 AM #49
Re: air source heat pump:how to make water reach 80℃?
Every IP have protection peroid,this is,maybe today it's is IP,tomorrow is know-how/knowledge, so during the protection peroid, illegal usage is forbidden ........
-
11-07-2010, 10:42 PM #50
Similar Threads
-
Water Source Heat Pumps DIY
By u4ia2000 in forum Heat PumpsReplies: 32Last Post: 10-11-2009, 09:16 PM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
Change my heat pump to water source
By tinkerer in forum Heat PumpsReplies: 14Last Post: 15-11-2008, 07:22 PM -
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
Water Source Heat Pump
By aliugur in forum FundamentalsReplies: 1Last Post: 02-06-2002, 03:24 PM