Re: Altherma frequent compressor cycling
Good idea.
Although your flow indicators are working the measurement of the return loop temperatures would help you to balance the system better. You may actually have a short circuit through part of the system which will encourage early compressor shut down.
With the system running, work from the index fully open circuit and compare with the next circuit. Adjust flow valve to achieve the same, or closely similar, return temperature. Proceed through the whole system until all returns are at the same temperature.Last edited by Brian_UK; 02-03-2010 at 11:19 PM. Reason: Spelling and meanings
Brian - Newton Abbot, Devon, UK
Retired March 2015