19-01-2010, 10:48 PM #1
Fujitsu AOY90TPAMF
Hello all,
I have a Fujitsu AOY90TPAMF which is showing no faults at the controller, but the condensing unit wont function in heating or cooling. The outdoor pcb has Led1 flashing constantly, and Led5 is flashing six times. I have tried to get a service manual from Fujitsu tech, but it still hasn't turned up. I tried to force the heating mode via the dip switch, but still nothing functioned. Any ideas welcomed, and a service manual would be gratefully accepted. I think the pcb may be goosed, but without being able to check anything, i don't want to say for sure. I weren't impressed with the Fujitsu technical helpline. Cheers, Andy C.
-
21-01-2010, 07:37 PM #2
Re: Fujitsu AOY90TPAMF
A quick update, i managed to find a service manual, and after a bit of reading and checking, found the outdoor pcb is goosed. A new pcb is on order, 7 - 10 days from Spain. Fujitsu tech helpline weren't much help when i finally got through to them.
Andy C.
-
08-02-2010, 10:55 AM #3
Re: Fujitsu AOY90TPAMF
We have replaced the outdoor board with a brand new one, and we are getting exactly the same fault. If anyone can shed some further light, i would be most obliged. Thanks in advance. Andy C.
-
08-02-2010, 11:48 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
08-02-2010, 12:48 PM #5
Re: Fujitsu AOY90TPAMF
Thanks Nike, we have carried out several checks to ensure the power supplies are correct. There is little chance of noise/ interference within the cabling, although we haven't checked. I have just ordered a new signal pcb, and will be changing it in the near future, based on advice given by a Fujitsu engineer.
-
08-02-2010, 01:26 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu AOY90TPAMF
Outdoor unit circuit board error 1
1. Error occurrence condition:Possible causes:Communication between control printed circuit board and communication printed circuit board of outdoor unit isn't performed correctly.2. Relevant operation1) Current operation is continued. Error is displayed on LED of outdoor unit.3. Clearance
2) If error is kept for 90 seconds since error occurs, new communication error (1F) occurs.The communication between control printed circuit board and communication printed circuit board of outdoor unit is performed correctly.
1. Effect of extraneous noise:1. When power is turned off, and turned on again:2. Outdoor unit communication PC board insertion is faulty.
1) If error doesn't occur, printed circuit board is normal. Then, remove noise sources near outdoor unit.
2) If error occurs again, remove noise sources and take measure with the following countermeasure No.2 and 3.2. Check the insertion of outdoor unit communication printed circuit board.3. Printed circuit board is faulty.3. Replace printed circuit boards with the following procedure, and check the operation.Your only "fault" in this is for not following procedure exactly as said in manual. It could save you one (much more expensive) PCB.
(1) Replace outdoor unit communication printed circuit board
(2) Replace outdoor unit control printed circuit board
-
08-02-2010, 04:22 PM #7
Re: Fujitsu AOY90TPAMF
Thanks again Nike, we have tried on numerous occasions to obtain a service manual for this unit, but Fujitsu being Fujitsu, cannot, or are unable to send us a copy of one. We shall carry out the necessary checks to ensure there are no noise issues.
It is a site we have recently inherited, which has had countless faults on the system over the years, mainly due to poor installation (mainly leaks and moisture).
Similar Threads
-
Fujitsu VRF AOY90TPAMF
By Daz man in forum Air ConditioningReplies: 2Last Post: 29-10-2009, 06:55 PM -
your opinons on fujitsu please
By acgibo in forum Air ConditioningReplies: 18Last Post: 26-08-2009, 05:06 PM -
Fujitsu VRF
By AbsoluteWDJ in forum Air ConditioningReplies: 14Last Post: 25-04-2009, 04:27 PM -
fujitsu wall mount volt free relay
By mike live in forum Air ConditioningReplies: 3Last Post: 09-04-2009, 08:26 PM -
Fujitsu or not?
By LRAC in forum Air ConditioningReplies: 14Last Post: 29-08-2007, 09:45 AM