Results 851 to 896 of 896
Thread: AWHP superheat & sub-cooling
14-09-2009, 01:56 AM #851
Re: AWHP superheat & sub-cooling
Each has its advantages.
Placing the superheater up front is more effective at adding superheat, but then the air entering the evap will be a little cooler, reducing the evap capacity gain.
Placing the superheater after the evap maximizes evap capacity, but there may not be enough temp difference to effectively dampen the hunting at low load.
It would be preferable to have the superheater after... if it can do the job.Last edited by Gary; 14-09-2009 at 02:02 AM.
14-09-2009, 02:06 AM #852
Here's a thought for you:
Hot liquid ex condenser, into front row of an evap coil.
Sub-cools liquid & heats up incoming air-stream. This air can now operate on evap/superheater & may be useful under cooler ambient air conditions. Less issues with defrosts, I'd think.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
14-09-2009, 02:24 AM #853
This would transfer the heat from the liquid to the refrigerant flow in the evap coil. I'm not sure this would raise the coil capacity... but I could be wrong.
The key to all of these configurations is the dT,air. If the delta-T is higher, then more heat is being removed from the air, therefore the coil capacity is increased.Last edited by Gary; 14-09-2009 at 02:28 AM.
14-09-2009, 03:07 PM #854
VIC / SGHX re-visited
I have listed a few simulations run in Coolpack, to re-test the concept of VIC, or SGHX, as I was finding that all the gains in the liquid sub-cooling, were essentially just forcing the evap to work harder, by reducing entry vapour fraction at entry.
No SGHX
30% thermal efficiency
50% thermal efficiency
75% thermal efficiency
100% thermal efficiencyEngineering Specialist - Cuprobraze, Nocolok, CD Technology
14-09-2009, 03:10 PM #855
The above calculations assume no line losses, or compressor external heat loss.
It can be seen that with more heat interchange from liquid line to suction line, that the COP does improve, but with astronomical increase in compressor discharge temperature.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
14-09-2009, 04:06 PM #856
14-09-2009, 04:32 PM #857
Not at all. I thought that Coolpack was usually received as being an authority amongst many hvac folks, It is easy to show up the results graphically, with little fuss. The log(p)-h diagram is an easy background to discuss the effect of any cycle changes, as well.
My simulator turns out some 10 pages for each such run - right down to individual fluid properties at each point in the system.
14-09-2009, 04:38 PM #858
Are we making any progress?
14-09-2009, 04:54 PM #859
14-09-2009, 04:59 PM #860
14-09-2009, 05:27 PM #861
15-09-2009, 01:10 AM #862
I don't understand why everyone wants to equate the VIC with the SGHX. They are NOT the same thing.Last edited by desA; 16-09-2009 at 07:47 AM. Reason: Edited by desA
15-09-2009, 02:05 AM #863
The VIC effectively increases the coil capacity without the high discharge temp.
Seems like a big difference to me.Last edited by Gary; 15-09-2009 at 02:07 AM.
15-09-2009, 01:37 PM #864
15-09-2009, 03:13 PM #865
Hmmm... the load would have to drop sufficiently to deplete the surplus liquid before the VIC could go 2-phase.
15-09-2009, 03:43 PM #866
15-09-2009, 04:32 PM #867
We have a variety of solutions available for resolving any hunting/floodback issues.
I feel confident that we can shift both flash elimination and superheating duties to the VIC, resulting in very substantial evaporator capacity increases.Last edited by Gary; 16-09-2009 at 05:57 AM.
16-09-2009, 12:45 AM #868
By mutual consent, the VIC technical discussions will now be continued in an alternative area.
The AWHP thread will continue with development & testing of the remaining areas still left to explore on the current lab heat-pump, with specific reference to superheat & sub-cooling as referenced at the start of this thread. There are still a number of open questions left to explore.
If anyone is still specifically interested in the VIC concept, please contact the authors Gary, or desA for further details, per private mail.Last edited by desA; 16-09-2009 at 12:58 AM.
16-09-2009, 12:50 AM #869
Another thing to notice is that, in general, the cold air outlet temp is rarely colder than the superheated refrigerant outlet temp. In other words, very little 'temperature cross' occurs.
My commercial evaps do actually have around 1-1.5'C temp cross, but the lab machine can't get there - inefficient coil design.
What is the approach temp on your commercial evaps?
Approach = 7.05-7.6K
Tcross ~ -0.8 to -1.4K (ie. air leaves evap Ta,out colder than superheated refrigerant outlet Te,sup)Last edited by desA; 16-09-2009 at 12:54 AM.
16-09-2009, 06:19 AM #870
Has the second lab unit, with the 3-tiered condenser, been modified for testing yet?
16-09-2009, 07:54 AM #871
^ Not yet... I've continued on the 2-tiered unit, running it for protracted runs to test the stability of recent changes over time & under varying atmospheric conditions.
On that 3-tier heat-pump, I'll have to also re-wire back to single-phase - so. I'll have to get my head together for that series of mods.
I'll plan do that after a trade show I need to attend in BKK during early October. This may be a good time to introduce a bunch more changes as well. I also have a spare plate HE on hand that will knock the socks off the 3-tiered condenser.
Welcome VIC...Last edited by desA; 16-09-2009 at 08:40 AM.
16-09-2009, 02:34 PM #872
TXV hunting
I've been doing a study around Magoo's rule for selecting evap superheat as a function of TD.
The suggested rule for evaps is : SH = (0.6 -> 0.7)*TD
I let the multiplier, here 0.6 -> 0.7 be a variable (let's call it beta), & observed that Ta,out is generally Te,sup (evap outlet temp) plus, or minus another variable - lets call it alfa.
Plug all this into the relationship for evap heat-transfer:
Q'e = (UA)*dTlm
and out comes something very interesting - when the value of beta is determined. I expected a single value to pop out & land somewhere in the range of 0.6 - 0.7 .
In all cases, the relationships show that beta can take on two (so far) values - in other words, there is a low value of SH, or a high value of SH, that will give the same answers for the heat-transfer equation. Some of this must stem from the non-linearity of the dTlm term. This is termed as 'bi-stability' in mathematical terms.
Now, can I ask the question again:
What is TXV valve hunting & what are the observed symptoms?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
16-09-2009, 07:06 PM #873
Keep in mind that a TXV is a proportional control, as opposed to PI or PID. There is a reaction time involved as well as the magnitude of reaction (orifice size). If the orifice is undersized for the current load, the reaction will be insufficient to close the offset. If the orifice is oversized for the current load, the reaction will be too great for the bulb to sense and moderate within the time constraint thus the mass flow will oscillate beyond the TXV's ability to progressively decrease the oscillations, driving the oscillations to the maximum.
hunting = maximum oscillation
I'm thinking the above is probably true of all proportional controls.Last edited by Gary; 17-09-2009 at 02:00 AM.
17-09-2009, 01:51 AM #874
^ Thanks, Gary. This makes sense.
Now, I wonder if these minimum & maximum oscillation bounds would correspond to the two beta (=SH/TD) values that an evaporator naturally can swing to?
I've done further research on this bi-stability phenomenon for the evap characteristic & it does seem to be one of the things that contributed to early CO2 system bi-stability problems.
What seems to be showing up is that there are two scenarios:
1. Low fan speed, large dTa => lower beta value;
2. High fan speed, small dTa => higher beta value.
So, then, it seems that the SH selection for a particular evaporator configuration & at a particular operating point, will have to be selected carefully.
I have a feeling that the beta=0.6->0.7 rule probably works well in cold-room situations, or indoor air-conditioning applications where TD is more moderate. For heat-pumps, this value may very well move to a more appropriate range, suitable for the large TD's experienced in AWHP applications.
Let's see where this all goes.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
17-09-2009, 03:43 AM #875
Excellent description "well done"
With the 2 biggest process variables being Ta(rh) and Tw (water in) both underfeed and overfeed are likley to occur on a unit this size (money limited)
I would suggets that you simulate at your design ambient/water limitations, ensuring that at these points your are within what you feel is acceptable liitations on the refrigeration machinery.
I then would look at system optomisation at a set of conditions, that are accepted as a standard in your area. I know this is a commercial issue, but at the end of the day you are developing a commercial product (finacially speaking) You then have one less variable to worry about
17-09-2009, 04:08 AM #876
17-09-2009, 04:29 AM #877
To better understand proportional controls, we need to start with the concept of offset.
If we adjust the TXV for optimum superheat under optimum conditions, there will always be an offset under non-optimum conditions.
If the heat load exceeds optimum, the bulb temperature increases which in turn opens the valve and increases the mass flow. But there is a catch22.
In order to match the increased load, the valve must remain open, but the valve cannot remain open without higher superheat as it is the superheat that opens the valve.
This 'tug of war' ends up in a compromise with the superheat higher than the optimum value. This difference between the actual superheat value and the optimum superheat value is the offset. The further from optimum load conditions, the greater the offset.
For the same reasons, there is always a negative offset under lower than optimum heat load conditions.Last edited by Gary; 17-09-2009 at 04:34 AM.
17-09-2009, 04:36 AM #878
The main issue I am raising here, in terms of the evap superheat issue, is that the evaporator is itself an unstable device - with the ability to 'select' a preferred operating state, given the correct set of prevailing conditions at the time. This is a symptom of bi-stability.
Now, we aim for a low(ish) SH to either suit the Magoo rule (0.6-0.7)*TD, or a slightly lower multiplier, or 7K.
Now, I've checked the (0.6-0.7) rule against low TD (10K) evap figures & it fits perfectly. In this case, there is almost NO bi-stability evident as the low TD drives the two beta (=SH/TD) values close together.
It is an entirely different matter when you start moving into high TD territory - here the bi-stability really begins to kick in.
The issue here is how to manage this in a safe, sane manner - while still keeping the compressor within safe bounds. In other words:
What should the appropriate SH (or beta=SH/TD) value be for high TD conditions?
This some new ground we are exploring here, of this I'm sure. Remember, Japan's local conditions are far more moderate than SE Asia.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
17-09-2009, 04:37 AM #879
People who calibrate proportion thermostats are all too familiar with offset. You calibrate the stat perfectly one day and the next day it is not maintaining the setpoint temp, because the weather changed. There is an offset between actual temp and setpoint temp.
17-09-2009, 04:40 AM #880
17-09-2009, 04:56 AM #881
The question is really how can we control the system, if the system is out of control, At present you limiting performance based upon the compressor manufactures envelope.
Take a step back it is a compressor, (larger systems are designed this way)
Say for instance Te is 25C superheat is 20C Tc is 45C, will this cause a problem?
Low compression ratio,
High mass flow
Is the motor over current?
Is the discharge overtemp?
If no, is there a problem? (apart from outside specs)
How long would this situation occur?
At some point a line in the sand has to drawn for best performance, component protection, is covered by your designated limits of your design
17-09-2009, 04:57 AM #882
And then came electronic controls with proportional/integral (PI) and proportional/integral/derivitive(PID). These are strategies for reducing the offset.
17-09-2009, 05:07 AM #883
17-09-2009, 05:37 AM #884
In general, Copeland wants minimum 11K superheat at the compressor inlet (although this may be different for scrolls). So... I guess the correct answer would be, the superheat at the bulb should be as low as possible, but not low enough to result in less than 11K superheat at the compressor inlet nor low enough to cause hunting, under the lowest load conditions (maximum negative offset).
My experience would indicate that the formula is upside down for high TD coils, that the superheat should be .3*TD to .4*TD.Last edited by Gary; 17-09-2009 at 06:19 AM.
17-09-2009, 06:16 AM #885
SH, first priority is to ensure "No Liquid return" Max SH is 25C, but not at all conditions, Bigger the compression ratio the smaller allowable suction sh, (lower discharge) smaller comprssion ratio higher allowable SH. All limited by motor current.
I would say if your dicharge temp was under 105C and your moter current was 5% less than the name plate FLA, you would be pretty safe.
17-09-2009, 06:34 AM #886
17-09-2009, 06:38 AM #887
Can handle, P & PI ,"D" always ****s me up, "thanks" for auto tune
1. PID are not always the best option;
2. Autotune functions can have absolutely disastrous consequences - if misapplied. Be well warned.
Unstable processes, with inherent dead-time, are the control engineer's nightmare - if, of course, they understand control philosophy properly.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
17-09-2009, 06:48 AM #888
1. ARI - SH 11.1K ; SC 8.88K
2. EN12900 - SH 10K; SC 0K
They also cut minimum evap temp with 10K suction SH & 25'C suction gas return.
Other suppliers are similar, but have some variations on this general theme.
How would the original concept of SH 7K fit into all of this?
17-09-2009, 06:53 AM #889
Fair comment.
Max SH is 25C, but not at all conditions,Did you mean to say max temp return is 25'C, or really max SH is 25K?
I would say if your dicharge temp was under 105C and your moter current was 5% less than the name plate FLA, you would be pretty safe.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
17-09-2009, 07:08 AM #890
Another good point, I can say that I have never had this issue arise (blown a few up due to floodback), I see these issues as going through a transision to reach design which should be within limits.
I do attempt to keep my machines within operatinal limits (somewhat easier the bigger you go) but I am also aware that occassionally we are going to move outside, I do not stretch compression ratios, I do not mind reducing compression ratios (within limits) higher Te, as long as Tc is low (motor output limit)
I do not mind high suction super heat as long as I have low compression ratios.
17-09-2009, 07:44 AM #891
17-09-2009, 09:09 AM #892
17-09-2009, 09:09 AM #893
17-09-2009, 11:34 AM #894
Gary - It would be really interesting if you could expand upon this offset. Why and how does the offset become either positive or negative under different heat loads when it is the SH itself that is the control parameter? Are you referring to a change in deltaP across the evaporater at differant flow rates or some other phenomena?
ChefLast edited by Chef; 17-09-2009 at 11:38 AM.
18-09-2009, 12:55 AM #895
I'd like to thank everyone who has been involved in this thread, it has been a privilege being able to debate back & forth with so many members with such extensive knowledge.
One thing that has become apparent through all of these many pages is that there are many different ways to arrive at a solution for any given RHVAC-related system - some better than others, others applicable under the circumstances in which they operate.
I wish the very best to all the contributors & trust that any further readers learn a great deal from the contents of this thread.
I wish you all the very best. My personal questions originally asked, have been answered - as have reams more.
Take care:
Gary, Magoo, Chef, mad_fridgie, & anyone else I may have missed. A huge thanks to Gary for his many hours of patience & practical advice.
I think we're done...Engineering Specialist - Cuprobraze, Nocolok, CD Technology
18-09-2009, 05:07 PM #896
At the request of the original poster, desA, this thread is now closed.
If you have any other viewpoints or questions similar to the original post then do please start a new thread.
BrianBrian - Newton Abbot, Devon, UK
9 superheat & subcooling scenarios
By nike123 in forum FundamentalsReplies: 39Last Post: 19-07-2011, 03:16 AM -
Superheat and Subcooling
Low superheat and sucooling
By jayaeros in forum Trouble ShootingReplies: 23Last Post: 05-07-2009, 06:21 AM -
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM