Discharge head cooling fan necessary?
Lately we replaced a compressor in blast chiller. It was reconditioned Bitzer compressor 6 cylinders 22 kW cooling power. This unit was used only as a hold temperature chiller (+2 C). My question is: because the compressor they send us was without head cooling fan , could we used it at that system or should we wait for a next compressor with the fan fitted on it? Is that fan very important and the compressor really could be damaged because working without it?
thanks
-
20-07-2009, 11:24 AM #2
Re: Discharge head cooling fan necessary?
Head cooling fan is required to keep the discharge end temperatures below 140 deg c .these are needed when the compressor operates on a large comp ratio & compressor`s operating parameters are beyond the operating envelope . Hence check the application ; condensing temp , evap temp & refrigerant used . These parameters can tell you whther you need the fan or not. At times keeping the overall superheat low might help. But best way is to check through bitzer software. If you can communicate these , i can check through bitzer program . Mention the compressor model too .
-
13-08-2009, 05:24 PM #3
Re: Discharge head cooling fan necessary?
Sorry for delay. Thank you very much for your answer. I found it easy explained. The fan is needed when compressor works at temperature under 0 Fahrenheit. Simple and easy in this case
regards
Similar Threads
-
Screw discharge cooling
By Volnei in forum Industrial CompressorsReplies: 13Last Post: 05-11-2008, 09:24 AM -
448 Head Cooling
By keepitcool in forum NH3Replies: 5Last Post: 06-06-2008, 06:38 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
suction and discharge head for parallel compounding compressors
By herman in forum CommercialReplies: 1Last Post: 11-10-2006, 08:32 PM -
Head cooling
By Peter_1 in forum IndustrialReplies: 27Last Post: 18-03-2004, 09:07 PM