05-07-2009, 04:19 PM #1
Relay sparks!!!! cooler not going cold!!!
Hello
I have a 4 door dumper fridge it is not cooling.
It is a commercial fridge stainless steel Not that that matters much.
Anyway the complaint is it is not cooling, There is some ice build up on the back of the evaporator.
I have checked the pressures and they seem to be correct.
The compressor is very very hot and also is the condenser (75 degrees C).
So i have checked the relay.. It clicks and there is a blue spark when it starts.
The compressor starts as well. However within a second there is a second spark inside the relay....
I am thinking that the relay is faulty and will need changing
any thoughts please let me know... Relay or capasitor?
But the Compressor is working BUT HOT
-
05-07-2009, 04:38 PM #2
Re: Relay sparks!!!! cooler not going cold!!!
Evap air in temp
Evap air out temp
Low side pressure/saturated suction temp
Suction line temp at TXV bulb
Cond air in temp
Cond air out temp
High side pressure/saturated condensing temp
Liquid line temp at receiver/condenser outlet
-
05-07-2009, 04:43 PM #3
Re: Relay sparks!!!! cooler not going cold!!!
All I can say is that the evap temp in general is 8 degrees C...
The con temp is 75 Degrees C.
On this fridge I can only check pressures via a service valve on the top of the comp...
Dont have valves on high side and the low side.
Not a very big comp
-
05-07-2009, 04:55 PM #4
Re: Relay sparks!!!! cooler not going cold!!!
We need as many of these temps/pressures as you can get.
-
05-07-2009, 04:58 PM #5
Re: Relay sparks!!!! cooler not going cold!!!
If relay that "sparks", it is evidently not good already.
The burning relay, however, may be only a consequence of another fault.
Maybe RUn capacitor bad (if such there is), or the compressor is "braking" during runtime, both making the start relay constantly switching on and off the START capacitor.
Fridge is most probably heavily overloaded.
-
05-07-2009, 07:29 PM #6
Re: Relay sparks!!!! cooler not going cold!!!
hi
size of compressor and ***** is it original
were did u measure 75degree if after the drier u must check if the condenser is clean if so air in &air out.
check compresser amp if its high it makes relay energises stsrt windings that what making relay sparks &comp hot
-
05-07-2009, 10:42 PM #7
Re: Relay sparks!!!! cooler not going cold!!!
Will have to check these out.
I will have to check the relay and cap....
The temp I have taken is on the condenser its self.
What I did notice was when I put the gage on the only service valve which is on the top of the comp some oil smelling stuff came out..
Could this be moisture etc......
-
05-07-2009, 11:02 PM #8
Re: Relay sparks!!!! cooler not going cold!!!
Last edited by Peter_1; 06-07-2009 at 12:33 PM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
05-07-2009, 11:58 PM #9
-
06-07-2009, 09:40 AM #10
Re: Relay sparks!!!! cooler not going cold!!!
So if I replace the cap would this help also changing the relay.
???????
-
06-07-2009, 10:58 AM #11
-
06-07-2009, 11:39 AM #12
Re: Relay sparks!!!! cooler not going cold!!!
I'd want to have an amp probe/current meter on the live feed to the compressor to see how much current it is pulling, sparking could be klixon operating if compressor is pulling too much power. And to test capacitor with a meter also.
Could be faulty relay/capacitor stopping compressor from running properly or faulty compressor (partly siezed, or shunted windings) making relay chatter. Or a blockage making the compressor run with too high a discharge pressure.
-
06-07-2009, 12:09 PM #13
Re: Relay sparks!!!! cooler not going cold!!!
-
07-07-2009, 04:29 AM #14
Re: Relay sparks!!!! cooler not going cold!!!
all relays were black in the old days hence no arcing was ever seen
mmm to beer or not to beer...........lets drink breakfast
Similar Threads
-
Cannot get the cooler to temp
By coolrunnings1 in forum FundamentalsReplies: 13Last Post: 27-06-2009, 07:51 PM -
Air cooler broken
By Rio69 in forum Trouble ShootingReplies: 5Last Post: 26-06-2009, 02:47 PM -
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
Hermetic analyzer " ANNIE" how do they work
By kengineering in forum Tools and CalculatorsReplies: 11Last Post: 02-03-2008, 06:10 PM -
voltage drop on relay
By Temprite in forum ElectricalReplies: 4Last Post: 30-01-2006, 07:55 PM