Thread: mitsi condensor fan
-
16-06-2009, 06:11 PM #1
mitsi condensor fan
hey fellas took over a job today from another engineer who has just changed the reversing valve,i was the one who got to run it up pressure test vac etc etc.Ran the unit up found power going to the solenoid valve which there shouldnt be thus making it go into heat mode i checked the several other units next to it which are the same. So what makes power now go to the solenoid??? next problem was the condensor fan only running very very slowly and very jerky as if power spikes going to it??.I changed the fan with another unit and also the module but still the fan wouldnt run correct going to change the boards over tomoz and see were it takes me. What controls the fan from the board there is a connector,black and white then from the module a red and orange cable??? then fan had no power in it i could even stop it with my hand very easily thanks alot
adam
Mitsubishi electric
Model No- PUH-P3YGAA
R407C
ajj
-
17-06-2009, 11:10 PM #2
Re: mitsi condensor fan
sounds like you have a faulty board and the relay that supplies the 4 way valve is latched...
-
18-06-2009, 10:49 PM #3
Re: mitsi condensor fan
cheers brunstar turned out to be the board thanks alot
adamajj
Similar Threads
-
Mitsi City Multi
By SatPro in forum Trouble ShootingReplies: 4Last Post: 25-01-2010, 03:43 AM -
Mitsi Heavy Fault
By coolments in forum Air ConditioningReplies: 2Last Post: 22-09-2008, 09:18 AM -
Mitsi Electric RP6AA Pump Fault
By gwilliamson in forum Air ConditioningReplies: 8Last Post: 15-08-2008, 05:59 PM -
Mitsi Lossnay Heat Exchanger
By sinewave in forum Air ConditioningReplies: 9Last Post: 05-02-2008, 05:55 PM -
Mitsi Problems
By Latte in forum Air ConditioningReplies: 9Last Post: 12-02-2005, 07:22 PM