09-06-2009, 11:54 PM #1
what went wrong with compresser
Hi all,this is my first post.am at the end of my first year of nvq 2 and i have been reading this forum for a while so i decided it was time i asked a question..(go easy people)
right.
i went with me mate earlier to a freezer coldroom that my mate had been to on sunday to do a bit of a clean on the condenser and a realy basic clean realy.now when i called back there with him today the compresser was cooked,it was showing 35 amps and he said the windings had gone.what i was wondering was what could,,,if anything he have done on sunday that would make this happen.i no am a bit green around the edges but if it was my freezer that he had been to i would be wondering what he had done when he called on the sunday.
sorry if this is a little confusing,i have it going round my head and was hoping you guys could shed some light on it.
many thanks
-
10-06-2009, 06:22 AM #2
Re: what went wrong with compresser
What ***** is there ? What are the settings of LP, HP protective relays ? Is it pump down on stop system ? Is not solenoid leaky ?
-
10-06-2009, 06:32 AM #3
Re: what went wrong with compresser
And has somebody checked up the actual work of the protective devices ?
You probably will not find out the reason untill you opened the compressor up for repair. When reinstaling the reparied, or a new one, having changed the oil, etc, check just everything before putting to work the system.
-
10-06-2009, 12:09 PM #4
Re: what went wrong with compresser
35 amps could be locked rotor amps,how big is compressor
mmm to beer or not to beer...........lets drink breakfast
-
10-06-2009, 05:58 PM #5
Re: what went wrong with compresser
the only suggestion i can come up with is that when cleaning the condensor he blew crap into the fan motor and it stopped .... or just out of luck ...it happens... welcome by the way!!!
-
10-06-2009, 07:18 PM #6
Re: what went wrong with compresser
cond fan faulty, comp electrics i.e. capacitor or relay, if three phase is there a phase down!!!!!!!!!!!!!!!!!
-
10-06-2009, 08:28 PM #7
Re: what went wrong with compresser
The compressor does usually benefit from condenser cleaning. Even if the condenser fan failed, the hp cut out switch should have stopped the compressor. I suspect it was just bad luck, but after replacing the compressor you should start a thorough investigation.
RTFM always thoroughly!
Vacuum sucks!
Sience rules!
-
13-06-2009, 02:33 AM #8
Re: what went wrong with compresser
35 amps the windings are still their.more than likely compressor has seized.only by metering the windings or visual inspection you will find out the true fault.i dont think your mate erred at all only that condenser could have done with a clean earlier,i generally blame the client as it is basic housekeeping
mmm to beer or not to beer...........lets drink breakfast
-
13-06-2009, 05:33 PM #9
Re: what went wrong with compresser
thanks for all the relys.he hasnt got back to me yet what the problem was,but ill let you know when he does..thanks..
-
14-06-2009, 01:19 AM #10
Re: what went wrong with compresser
The damage was probably done with high condenser temps, now you are picking up the result.
Similar Threads
-
Ice forming on compresser?
By jbomba in forum Trouble ShootingReplies: 12Last Post: 27-04-2009, 01:25 AM -
Compresser electricals - HELP me please!!!
By pjalchemist in forum ElectricalReplies: 38Last Post: 28-11-2008, 12:09 PM -
Can someone point what's wrong
By Peter_1 in forum IndustrialReplies: 30Last Post: 22-04-2008, 07:04 PM -
Wrong expansion valve installed
By kentbf in forum Trouble ShootingReplies: 29Last Post: 02-03-2008, 08:49 PM