01-06-2009, 03:48 PM #1
Calculating Tonnage of refrigeration machine
Hello all, i'm an engineering intern trying to calculate the tonnage of an electric brine refrigeration machine. I read the info on the motor and it's a: 223 amp motor, 2300 volts, 900 HP. Anyone know how to calculate tonnage?
01-06-2009, 03:50 PM #2
Re: Calculating Tonnage of refrigeration machine
That will not work. You need to find the operating conditions of the refrigeration system and a copy f the compressor manufacturers performance data.
Anything else is just a wild guess.If all else fails, ask for help.
01-06-2009, 05:05 PM #3
I have a list of real-time operating conditions:
Comp TEJ Bearing Temp Comp SEJ Bearing Temp Comp Thrust Bearing Temp Comp Oil Reservoir Press Comp Oil Temp Comp BRG Oil Supply Comp Back of Seal Oil Press Comp Oil Diff. Press Comp Discharge Gas Temp Comp Bearing Oil Supply Temp Gear/Motor Oil Supply Temp Motor Amps Cond. Enter Water Temp Cond. Exit Water Temp Cond Refrigerant Temp Cond Refrig. Press Evap Refrig. Press Brine Entering Temp Brine Leaving Temp Main Brine Loop Temp Evap Refrig. Temp Economizer Refrig. Temp Control Air Press Local Temp Set Pt. PID Out
I'm wondering if I can use the motor amps and voltage to get HP and use that to calculate tonnage..
01-06-2009, 05:08 PM #4
Sorry, here it is in list form:
Comp Oil Reservoir Pressure
Comp Oil Temp
Comp BRG Oil Supply
Motor Amps
Cond Refrig. Press
Evap Refrig. Press
Brine Entering Temp
Brine Leaving Temp
Evap Refrig. Temp
Control Air Press
Local Temp Set Pt.
PID Out
01-06-2009, 07:16 PM #5
all you need are these:
Cond Refrig. Press
Evap Refrig. Press
Convert the pressures to the saturation temperatures for the specific refrigerant used in the compressor. Now look these temperatures up on the compressor manufacturers performance charts. They list the compressor performance based on saturated inlet (suction) and condensing temperatures.If all else fails, ask for help.
02-06-2009, 01:34 PM #6
09-06-2009, 11:21 PM #7
Here is what I do. First you need to have the manufactures performance data at 25 different Suction and discharge temperatures. These are laid out in a matrix. 5 suction by 5 discharge. These will be shown as Tons of refrigeration and Brake Horse Power. By running these numbers through a nasty equation you can come out with that compressors performance at any given suction and discharge temperature. If the compressor has a VFD just use the speed as a direct multiplier. If the compressor is a screw and is running at a part load it is not a linear conversion. You would need to find out how the slide valve affects capacity at different positions. So 90% slide valve does not mean 90% capacity. There is a nasty equation for that too. Recips are linear.
advanced refrigeration technology
By Lc_shi in forum FundamentalsReplies: 10Last Post: 16-02-2011, 05:22 PM -
Smallest absorption refrigeration maschine and vapour-compression machine
By Masinchen26 in forum CommercialReplies: 8Last Post: 23-04-2008, 06:48 PM -
Calculating Refrigeration load for Cold room
By Sridhar1312 in forum CO2Replies: 1Last Post: 16-01-2008, 12:06 AM