flooded evaporator in screw chiller
Hi sirs
I've heard that some manufacturers apply flooded evaoprator design in their screw chillers. It's said that the COP is higher than DX system. But how about the pro and cons of flooded evaporator?
regards
LC
I hear...I forget;I see...I remember;I do...I understand
-
22-05-2006, 02:37 AM #2
Re: flooded evaporator in screw chiller
Hi LC,
For flooded units the following comments are applied:
Pros
- Higher heat transfer
- Potentially lower approach temperature with same surface area
- Almost no evaporator superheat that can increase vapor density and mass flow, hence increased capacity
- Liquid/vapor separation incorporated into design
- Easier ability to reduce discharge pressure
- Less low load operating problems (better turndown)
- Cooled fluid flows through tubes (easier cleaning if needed)
Cons
- More refrigerant is required
- Added cost for liquid/vapor separator
- Oil recovery method required
-
22-05-2006, 11:20 AM #3
Re: flooded evaporator in screw chiller
Hi Lc,
Most of my equipment is screw compressor & flooded type,some are shell & tube eveporator, but mostly PHE.
Better COP.
Guapo
-
22-05-2006, 04:36 PM #4
Re: flooded evaporator in screw chiller
Hi,
The item which you should be most concerned about is a loss of water flow condition. In flooded evaps, the tube bundle freezes and ruptures very easily if a loss of water flow condition occurs. We always suggested redundant proof-of-flow switches. We even had freeze-ups when the charge was blown, even though accepted practice [and instructions] was to operate the water pumps during this period.
If it is a R134a machine, once water gets into EVERYTHING, huge trouble as the oil is highly hygroscopic. Very difficult to clean eveything out to acceptable levels.
Good luck, bigJohn
P.S. not to worry anyone, "Blow the charge" is a factory term in current usage. Of course, nowadays, it is recovered.
-
23-05-2006, 01:52 AM #5
Re: flooded evaporator in screw chiller
HI guapo
Use plate heat exchanger as flooded evaporator? I don't know how to control the liquid level? pls teach me
rgds
LCI hear...I forget;I see...I remember;I do...I understand
-
23-05-2006, 02:42 AM #6
Re: flooded evaporator in screw chiller
LC,
If you go to this post: http://www.refrigeration-engineer.co...9&d=1147285803
You will find a sketch of a flooded PHE.
The liquid level is maintained in the vessel above the PHE. A simple float switch controlling a solenoid valve will work nicely. The flow rate into the vessel is controlled by a hand expansion valve.
-
23-05-2006, 12:24 PM #7
Re: flooded evaporator in screw chiller
Hi Lc,
US ICEMAN is correct, simple as that. You can also control the level by electronic level controller for better performance. I think most of the packaged chiller now they use PHE.
Regards,
Guapo
-
24-05-2006, 01:05 AM #8
Re: flooded evaporator in screw chiller
hi guapo,
understand what you say
Where is the key tech of this type machine? Oil return \ level control or liqiud vapour separator? Could you offer me a system sketch of your screw machine. How about the COP bigger than DX evap?
thanks and regards
LCI hear...I forget;I see...I remember;I do...I understand
-
24-05-2006, 12:51 PM #9
Re: flooded evaporator in screw chiller
Originally Posted by Lc_shi
The unit has oil separator right after discharge, and on the top of the PHE there is a what we call surge drum. Surge drum we maintain the level of refrigerant, around 1/4. Since the suction line is on the top of the surge drum, only vapor will go to the compressor.
The PHE is full of refrigerant because the level is 1/4 on the surge drum which located on the top of the PHE, unlike the DX evaporator you have to left some space for your super heat.
Regards,
Guapo
-
25-12-2008, 02:00 AM #10
-
25-12-2008, 02:04 AM #11
-
25-12-2008, 09:30 AM #12
-
25-12-2008, 09:35 AM #13
Re: flooded evaporator in screw chiller
Attached the principle of a screw chiller!
-
31-12-2008, 12:03 PM #14
-
31-12-2008, 12:08 PM #15
Re: flooded evaporator in screw chiller
can anyone tell me how to select DX ammonia evaporator. If i select Pumped system evaporator and convert in to DX System , will there be any changes in the capacity.
srini
-
31-12-2008, 07:05 PM #16
-
31-12-2008, 07:07 PM #17
-
04-01-2009, 04:36 AM #18
-
04-01-2009, 04:38 AM #19
-
27-05-2009, 01:23 PM #20
-
27-05-2009, 09:43 PM #21
-
27-05-2009, 10:10 PM #22
Re: flooded evaporator in screw chiller
Of course I can, but what is inside what you call "GAS PUMP"? Are the solenoids interlocked and how are they managed? How is the geometry of the oil pipe in the evaporator vessel?
-
29-05-2009, 03:38 PM #23
Re: flooded evaporator in screw chiller
the dotted line in the evaporator is there to indicate the level,not a pipe, maybe that helps! The solenoids help to suck in and push out the oil.
-
29-05-2009, 04:57 PM #24
-
29-05-2009, 08:48 PM #25
Re: flooded evaporator in screw chiller
As for the controls, it's managed by a CH530. (That's trane)
-
05-07-2010, 05:37 AM #26
Re: flooded evaporator in screw chiller
Similar Threads
-
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
DX vs. flooded chiller
By Nirmalya in forum IndustrialReplies: 10Last Post: 16-08-2006, 07:09 PM -
Mcquay PES Flooded Water Cooled Screw Chiller
By Brian in forum Technical SpeculationsReplies: 4Last Post: 05-07-2006, 09:43 PM -
Screw Chiller commissioning
By iceman007 in forum Industrial CompressorsReplies: 7Last Post: 11-01-2006, 01:19 AM -
York Open Drive Screw Chiller
By Cofreth in forum Air ConditioningReplies: 4Last Post: 24-10-2005, 02:17 PM