    Amcoraire



    anyone use this brand? can't find much info, i've got a 24,000 btu inverter unit it works for about 2 hrs. then flashes p8 for lack of ***** or conversion valve failure this is a new unit, the heat and cold work but on cooling it flashes p8 it's setup correctly as far as my 410a slidechart goes

    on another note does -20 fahrenheit sound right for suction temperature?

    thanks everybody



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Amcoraire

    What type of service is it doing, freezer or cooler?

    Mind you, re-reading your post you are using R410a, so is it an air conditioning unit ?

    If it is then your suction temperature is way too low.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2009
    Location
    west l.a
    Posts
    16
    Rep Power
    0

    Re: Amcoraire

    It's a mini split a/c made by amcor (which is made by tadiran? anyone?) any reliability ratings on amcor brand or opinions?

    I'm going to the site on tuesday to recover refrigerant and recharge with the correct weight, and see what happens from there.

    I don't work with many inverter a/c, i've learned from this great website that the slide chart does not work with inverter's

    thanks everyone

  4. #4
    Join Date
    Mar 2009
    Location
    west l.a
    Posts
    16
    Rep Power
    0

    Re: Amcoraire

    I have more info on this inverter a/c it will randomly when it restarts create a super low suction pressure I actually measured it at 15" of vacuum and shortly after it shut off with the code for low refrigerant or bad reversing valve, I know for certain it's not low on refrigerant but would a bad reversing valve cause this? even though it never gets activated (these 3 a/c's will never see heat mode,)

    The unit i spent my weekend with works all day great but when outside temp goes down this problem seem's to happen with this one, is this a symptom of low ambient temperature?
    even though these are rated to 4 degrees in cooling mode
    and it's about 55 fahrenheit outside maybe a little less

    Or could these things be so poorly made that there clogged up with trash? causing a restriction?

    The amcor tech rep says theres a known problem but his only answer is to exchange the condensing units which will also end my warranty and i'll end up with 3 more with the same problem!

    sorry to ramble on i've installed dozen's of mini splits and never had a problem so this is really bugging me!

    I really need some ammo to fire back at the tech rep any and all information would be greatly appreciated!!!!!!!!!!!!

    Thanks

  5. #5
    Join Date
    Mar 2009
    Location
    west l.a
    Posts
    16
    Rep Power
    0

    Re: Amcoraire

    Well i'm changing 2 of these out for samsung's but the liquid line for the samsung is 1/4 instead of 3/8 can I just reduce the ends of existing lineset?


    this is a $5000 loss to me!! don't buy amcor they suck!!!!!!!!!!!!!!!!!!!!

    Thanks for any responses.