    Question Effect of Evaporator Volume on the Performance of Domestic Refrigerator
    Hello friends,
    Will someone help in explaning the following .........
    What will be the impact on Evaporator Inlet Temp & Evaporator Outlet Temperature if we increase or decrease volume of Evaporator by 10% approx in a domestic refrigerator
    All other components & parameter are same
    Split Croatia
    6,151
    Re: Effect of Evaporator Volume on the Performance of Domestic Refrigerator
    Quote Originally Posted by eager View Post
    Hello friends,
    Do you mean evaporator active surface increase of 10%?
    Nov 2006
    India
    11
    This is a Roll Bond Panel type Evaporator, there is no change in surface area of panel, only change is in the internal volume of passage for refrigerant
    I would suggest that the cooling capacity will decrease.
    Nov 2006
    India
    11
    Thanks Brian
    But it will be better if i may know the logic behind this
    Aug 2005
    5,302
    May I ask the reason for this question? If you change the internal volume of the refrigerant circuits in the evaporator, what do you expect to happen?
    Thanks Brian
    Very simple logic really - less pipework for refrigerant means less cooling surface.
    Nov 2006
    India
    11
    Well, this is because Evaporator is from some supplier other than the original Supplier & its volume is more than the original one
    Jun 2005
    California
    394
    Of course this must apply otherwise all bets are off
    Aug 2005
    5,302
    Since we do not have a lot of information to review here are some basic points to be aware of:
    a) The flow path(s) of the refrigerant through the evaporator are called circuits. A circuit is the complete length of this flow path. There may be more than one in any evaporator. However, since you said this is a domestic refrigerator I would assume there is only one circuit with a single cap tube feeding the evaporator circuit.
    b) If the internal volume of the circuit is greater than the original one I would again assume the circuit diameter is larger (or it could be longer). This can affect either pressure loss or heat transfer capacity. Either may cause a loss of capacity.
    c) The capacity of the new evaporator should be available from the new manufacturer. They should state the pressure loss of the evaporator circuit and the overall heat transfer capacity also. If the new evaporator has performance and pressure loss characteristics different from the original then the system performance will be different even with the same compressor, condenser, cap tube, etc.
    The only way to be 100% sure the new evaporator will perform as desired is to test the refrigerator with the replacement evaporator.
    Nov 2006
    India
    11
    Thanks for your answer
    rollbond's Avatar
    rollbond Guest
    It will depend on the difference of internal volume between the new evaporator and the previous one.
    Due to manufacturing constraints, the tolerance of internal volume of a roll bond evaporator is most of time +/-10%. This tolerance has been accepted by the refrigerators manufacturers for years and the impact on the performances is low.
    Of course, if the volume is out of this tolerance you should ask to your supplier to decrease the internal volume for the next order.
    Dec 2008
    UAE
    42
    171
    The effect of internal volume on ref. performance is as
    1. Once you reduce the internal volume and keep the secondary area same then, the superheat of eva increases/no change, but during practical situation the evaporator temperature go up, means superheat increases, hence reduces the cooling capacity.
    2.If you want to use a big evaporator or say higher in internal volume, then there is not much change in Superheat. also, if you dont change the charge (Refrigerant) quantity, then no change in cooling performance but if you slightly increase the charge qty as well then you get better cooling performance.
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. Replies: 2
    Last Post: 26-01-2008, 12:48 AM
  3. pressure release duration in refrigerator
    By junhonguk in forum Technical Speculations
    Last Post: 13-01-2008, 07:06 PM
  4. extra cooling on domestic refrigerator
    By ditchcrawler in forum New Technologies
    Last Post: 17-01-2005, 08:56 AM
  5. Domestic refrigerator coolant data
    By Paul in forum Fundamentals
    Last Post: 13-10-2001, 10:31 AM