06-02-2009, 08:09 PM #1
a/c split units pump down
hi guys,
how many small split systems out their can actuelly be pumped down? and if so is it like pumping down a normal sytem into a receiver after isolating it????
info please
-
06-02-2009, 08:40 PM #2
Re: a/c split units pump down
Hi Paul
The outdoor unit has a liquid line and a suction isolation valves (where the pipe work connects. connect your gauges to the bottom of the suction service valve, then close the liquid line. start the compressor via temp adjustment or plugging the contactor. The suction pressure will start to drop as the liquid is being held back by the isolation valve. Hold the contactor in untill u reach 3 psi.
then close the suction line..... job done.
careful with vrv's they need a complete reclaim you cant pump them down if they have extended pipe work, as extra charge is added to fill the pipe.
hope that helps mate
-
06-02-2009, 08:50 PM #3
Re: a/c split units pump down
[quote=THE WOMBAT;134739]Hi Paul
The outdoor unit has a liquid line and a suction isolation valves (where the pipe work connects. connect your gauges to the bottom of the suction service valve, then close the liquid line. start the compressor via temp adjustment or plugging the contactor. The suction pressure will start to drop as the liquid is being held back by the isolation valve. Hold the contactor in untill u reach 3 psi.
then close the suction line..... job done.
becareful if the split has extended pipe work, the longer the pipework the more gas is needed. the unit can only hold so much
careful with vrv's they need a complete reclaim, you cant pump them down if they have extended pipe work, as extra charge is added to fill the pipe. Make sure all the valves in the multi-controllers are open, otherwise u will trap gas in the evporator heads
hope that helps mate
-
08-02-2009, 06:53 PM #4
Re: a/c split units pump down
great explanatiom mate thanks alot
cheers
Similar Threads
-
Vrv
By tgoonter in forum Air ConditioningReplies: 4Last Post: 11-01-2011, 06:25 AM -
New Building, New Units!!!
By Fett in forum Air ConditioningReplies: 6Last Post: 19-11-2008, 03:43 PM -
Chinese built split units
By IanB in forum Air ConditioningReplies: 6Last Post: 06-07-2008, 07:58 AM -
Do you beleive in data of split units?
By jirhol in forum FundamentalsReplies: 4Last Post: 29-03-2008, 11:17 PM -
Highcool split air con units
By iceman007 in forum Air ConditioningReplies: 10Last Post: 31-05-2005, 12:31 PM