05-02-2009, 12:21 PM #1
Sharp Error codes
Hi guys
Looking for error code meanings for a sharp split System
AE-A249J
Outdoor board flashs
3 flashs 6 times & 1 solid
& then starts the process again
Thanks in advance
If its Does'nt Work Use a bigger Hammer
-
05-02-2009, 02:07 PM #2
Re: Sharp Error codes
AC abnormal current. There's a current detector on the outdoor PCB.
Check capacitor, check soft starter (wire up without s/s as per wiring diagram, you need to make up a lead from the capacitor to neutral with the soft start removed.)
I've done a dozen of these in the past month, it's nearly always the capacitor and/or quickstart 5
If the capacitor is good* and the soft starter is bypassed and the system still faults out, remove the lead that goes through the current sensing coil loop and check the amps when the compressor starts. If amps normal and compressor starts fine, then the PCB is faulty.
edit: of course if the amps are high the compressor is faulty.
*I had a capacitor that worked for 5 min then died when the cap heated up, so be sure the cap is good by using a decent meter and the cap is well within spec (I've had ones that were dud measuring at 35uF when they should have been 50uF), or use a spare 50uF test capacitor.Last edited by paul_h; 05-02-2009 at 02:16 PM.
-
05-02-2009, 02:32 PM #3
-
05-02-2009, 02:59 PM #4
Re: Sharp Error codes
[quote=paul_h;134505]AC abnormal current. There's a current detector on the outdoor PCB.
Check capacitor, check soft starter (wire up without s/s as per wiring diagram,
Any Chance of diagram
Thanks PaulIf its Does'nt Work Use a bigger Hammer
Similar Threads
-
Sharp Inverter error code
By karl957 in forum Air ConditioningReplies: 2Last Post: 29-12-2008, 01:30 PM -
Spare Parts for Sharp Units ? Trade
By S_Line in forum Heat PumpsReplies: 5Last Post: 20-11-2008, 08:31 AM -
Sharp inverter problem
By marc5180 in forum Air ConditioningReplies: 6Last Post: 17-06-2008, 05:28 PM -
A number for Sharp anybody?
By marc5180 in forum Air ConditioningReplies: 17Last Post: 04-05-2008, 01:47 PM -
Sharp A/c
By dakesojo in forum Air ConditioningReplies: 2Last Post: 11-06-2006, 10:02 PM