    Sharp Error codes



    Hi guys
    Looking for error code meanings for a sharp split System
    AE-A249J
    Outdoor board flashs
    3 flashs 6 times & 1 solid
    & then starts the process again

    Thanks in advance


    If its Does'nt Work Use a bigger Hammer

  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Sharp Error codes

    AC abnormal current. There's a current detector on the outdoor PCB.
    Check capacitor, check soft starter (wire up without s/s as per wiring diagram, you need to make up a lead from the capacitor to neutral with the soft start removed.)
    I've done a dozen of these in the past month, it's nearly always the capacitor and/or quickstart 5

    If the capacitor is good* and the soft starter is bypassed and the system still faults out, remove the lead that goes through the current sensing coil loop and check the amps when the compressor starts. If amps normal and compressor starts fine, then the PCB is faulty.
    edit: of course if the amps are high the compressor is faulty.

    *I had a capacitor that worked for 5 min then died when the cap heated up, so be sure the cap is good by using a decent meter and the cap is well within spec (I've had ones that were dud measuring at 35uF when they should have been 50uF), or use a spare 50uF test capacitor.
    Last edited by paul_h; 05-02-2009 at 02:16 PM.

  3. #3
    Join Date
    May 2007
    Location
    Australia
    Age
    39
    Posts
    73
    Rep Power
    18

    Re: Sharp Error codes

    Quote Originally Posted by paul_h View Post
    AC abnormal current. There's a current detector on the outdoor PCB.
    Check capacitor, check soft starter (wire up without s/s as per wiring diagram, you need to make up a lead from the capacitor to neutral with the soft start removed.)
    I've done a dozen of these in the past month, it's nearly always the capacitor and/or quickstart 5

    If the capacitor is good* and the soft starter is bypassed and the system still faults out, remove the lead that goes through the current sensing coil loop and check the amps when the compressor starts. If amps normal and compressor starts fine, then the PCB is faulty.
    edit: of course if the amps are high the compressor is faulty.

    *I had a capacitor that worked for 5 min then died when the cap heated up, so be sure the cap is good by using a decent meter and the cap is well within spec (I've had ones that were dud measuring at 35uF when they should have been 50uF), or use a spare 50uF test capacitor.
    Thanks
    got 2 dead units as well
    Never seen a sharp Ac before that...
    Comp windings & caps are good
    Thought it might be the soft starter ....
    If its Does'nt Work Use a bigger Hammer

  4. #4
    Join Date
    May 2007
    Location
    Australia
    Age
    39
    Posts
    73
    Rep Power
    18

    Re: Sharp Error codes

    [quote=paul_h;134505]AC abnormal current. There's a current detector on the outdoor PCB.
    Check capacitor, check soft starter (wire up without s/s as per wiring diagram,


    Any Chance of diagram
    Thanks Paul
    If its Does'nt Work Use a bigger Hammer

Similar Threads

  1. Sharp Inverter error code
    By karl957 in forum Air Conditioning
    Replies: 2
    Last Post: 29-12-2008, 01:30 PM
  2. Spare Parts for Sharp Units ? Trade
    By S_Line in forum Heat Pumps
    Replies: 5
    Last Post: 20-11-2008, 08:31 AM
  3. Sharp inverter problem
    By marc5180 in forum Air Conditioning
    Replies: 6
    Last Post: 17-06-2008, 05:28 PM
  4. A number for Sharp anybody?
    By marc5180 in forum Air Conditioning
    Replies: 17
    Last Post: 04-05-2008, 01:47 PM
  5. Sharp A/c
    By dakesojo in forum Air Conditioning
    Replies: 2
    Last Post: 11-06-2006, 10:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •