    Question Daikin Liquid Temp.



    Also what kind of liquid temp would you expect to get to get at 40 deg coutside, i am finding it hard to get under 12deg c liquid temp, and 28deg in the house, the unit has been on since 8:00 in the morning, so it should'nt be working so hard,

    Also i double checked my part numbers
    numbers are
    Indoor Unit FDYQ160KV1
    Outdoor Unit RZQ160KV4A

    Thanks again



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin Liquid Temp.

    The liquid temperatue you are measuring is part of the evaporator, as the expansion device is in the outdoor unit and is electronically controlled by the PCB.

    You don't say how big your house is or what the terminal devices are or the return path to the indoor unit etc.

    Here in the UK, many of the air conditioning units are designed to achieve 21C indoor when the outdoor temp is 27C, a 6K difference. You are achieving 12K so I would consider the unit is working quite hard.

    It is difficult to diagnose a problem from so far away though.... you may or may not have a problem.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Daikin Liquid Temp.

    AT 40°C outside I would think that you have exceeded the design conditions and must expect the indoor temperature to rise accordingly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Daikin Liquid Temp.

    Take into consideration that the outdoor unit has an additional subcooling heat exchanger (at least RZQ200C7W1B has it).

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin Liquid Temp.

    28 deg indoors well that is not too bad considering it is 40 deg, the unit sounds undersized to me. the reason the liquid line is so cold is that it is pre expanded and not a true liquid line.
    what is the floor area of the place? is the return air ducted off?, try feild setting 13-6-02 to give you more air flow on your indoor unit, i feel as though you maybe undersized or crap insulation in the house or a lot of glass.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin Liquid Temp.

    If unit is correctly sized and in full working order than it should work without problems till outdoor temperature doesn't exceed 46°C.

    http://www.affordair.com.au/equipmen...ted/ducted.htm

  7. #7
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin Liquid Temp.

    Most domestic ac is usually sized to track the oudoor temp <15 degC not maintain a setpoint.

  8. #8
    Join Date
    Jan 2009
    Location
    Melbourne
    Posts
    14
    Rep Power
    0

    Re: Daikin Liquid Temp.

    Quote Originally Posted by brunstar View Post
    28 deg indoors well that is not too bad considering it is 40 deg, the unit sounds undersized to me. the reason the liquid line is so cold is that it is pre expanded and not a true liquid line.
    what is the floor area of the place? is the return air ducted off?, try feild setting 13-6-02 to give you more air flow on your indoor unit, i feel as though you maybe undersized or crap insulation in the house or a lot of glass.
    Thanks Brunster i have increased the fan speed much better air flow in outlets further away from unit. the unit is undersized for my whole house, but it is zoned so i only have two zones on which are the main trafic areas, Do you a a list / book will all the dakin codes in it?
    Cheers

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Daikin VRV coil target temp during heating
    By mchild in forum Air Conditioning
    Replies: 16
    Last Post: 14-01-2009, 08:11 PM
  3. Temp over run with Daikin VRV-S
    By mchild in forum Air Conditioning
    Replies: 21
    Last Post: 14-12-2008, 03:19 AM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •