    Angry Automatically shutdown of Cu-A12CKP5 Air-conditioner



    Hi,
    When I turned on the indoor unit with the remote control, it run hard for approx. 1 second then slow down for 3-4 seconds, with the flap swinged ok. The cycle repeated itself for 5-6 times then the flap closed and both the indoor and outdoor units turned off. During the high - low cycle happening with the indoor unit, the outdoor unit compressor and fan seems to run smoothly.
    Thanking in advance for your assistance.

    Also if you have a copy (or link) for the service manual for this model Cu-A12CKP5 would be greatly appreciated.
    Regards,
    Henry



  2. #2
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    140
    Rep Power
    22

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner


  3. #3
    Join Date
    Jan 2009
    Location
    Sydney Australia
    Posts
    6
    Rep Power
    0

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Hi Narkom,
    Happy new year to you and your family. Thank you for your prompt reply. On the web-link you suggested, there is no service manual for this model Cu-A12CKP5 but Csu-a912CKPG.
    Thanks and cheers.
    Regards Henry

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Quote Originally Posted by civaro View Post
    Hi Narkom,
    Happy new year to you and your family. Thank you for your prompt reply. On the web-link you suggested, there is no service manual for this model Cu-A12CKP5 but Csu-a912CKPG.
    Thanks and cheers.
    Regards Henry
    http://www.nodevice.com/manual/newma.../get57700.html

  5. #5
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Problem is that the signal from the hall effect sensor in the fan motor needs to match up to a reference voltage.
    Problem is too fold.
    Bad regulation on the main PCB making the reference voltage fluctuate.
    which needs replacement but in some cases the fan motor will require replacement also.

    If it is a cash job, quote for both...

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Try the motor first. They're cheaper and a bad pcb won't stuff up a motor with one short test.
    Worst case senario, you need to come back with a PCB and replace both, either way, you need a new motor, but sometimes you don't need a new PCB.
    I'd never plug a new PCB into an old motor, if the motor is dodgey there's a chance the new PCB would be stuffed straight away.

    When I was changing them all over the place as chargeable jobs I always got both as it saves a lot of time, and time is money anyway.
    But my brothers cs-a12ckp stuffed up a week ago and I just tried changing the motor and it was fixed, no more problems.

  7. #7
    Join Date
    Jan 2009
    Location
    Sydney Australia
    Posts
    6
    Rep Power
    0

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Thanks Guys.
    I will quote for both (it may not be competitive when considering the new unit which comes with 5 years warranty). However i will keep you posted if the client would like to proceed with the repair. Do you have a copy of the manual for my reference?
    Regards
    Henry

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Quote Originally Posted by civaro View Post
    Thanks Guys.
    Do you have a copy of the manual for my reference?
    Regards
    Henry
    Click on the link kindly provided by Nike123 above.

  9. #9
    Join Date
    Jan 2009
    Location
    Sydney Australia
    Posts
    6
    Rep Power
    0

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Hi,
    I finally had the chance to find out that both main controller board and indoor fan motor were dud.
    1. Main Board: The pre-biased transistor Q03 which drives the solid state relay SSR01 went short circuit between Collector and Emitter, and
    2. The indoor fan motor heat-up badly.
    Thanks again for all your assistence.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Nice to see that someone goes to repair of electronics instead of simply swapping parts! Good work!

  11. #11
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: Automatically shutdown of Cu-A12CKP5 Air-conditioner

    Civaro,
    Interesting diagnoses.
    If the transistor is short driving the SSR, which drives the fan motor, how did the unit try 5 times and then turn it off again?

    Would it not run constantly?

    Good to hear you got it sorted though