11-12-2008, 11:44 AM #1
york chiller motor rotation error
hello can anyone help about chiller problem, its about this york maxe chiller that we are to startup.... when the chiller was to be started the error msg motor rotation would come up... weve already used a phase sequencer and checked the sequence... the chiller have a acrel adr3-800H motor protection in the starter.. weve tried to disable the phase sequence protection but the motor rotation still comes out.. even if we bypass QE its still the same... anybody have an idea???? the chiller is a york maxe yr model.. 350tons.
-
11-12-2008, 01:12 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: york chiller motor rotation error
Did you checked correct wiring inside of control panel? Do you have all three phases at phase control relay? Did you checked phase imbalance?
-
11-12-2008, 02:34 PM #3
Re: york chiller motor rotation error
well im just a beginner, actually im just an operator so i have no idea about that phase control relay. but the one who have done the wiring was our technician.. i have downloaded a manual of the said acrel ard3 motor protection, and tried to help our technician solve the problem. there was a p010 setting for the device which is the motor phase protection.. it was set at 8 which we changed to 1. (0 is disable, 1 is enable; but was set to 8) so we tried to set it to 1 and the motor run for about 8 secs, and then there it was again, motor rotation msg. it seems like the motor cant run in delta.. after secs of running in wye it stops and the msg appears in the chiller control panel...
-
11-12-2008, 04:01 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: york chiller motor rotation error
Then post link for that manual thru your visitor message!
Last edited by nike123; 11-12-2008 at 04:04 PM.
-
11-12-2008, 04:08 PM #5
Re: york chiller motor rotation error
Who is the manufacture of the starter? Is the motor turning the direction that is shown casted on the compressor? What is the message displayed on the control panel of the chiller?
I seems to me that the starter may not be seeing the motor current properly, then timing out, and not transitioning.
-
11-12-2008, 09:17 PM #6
Re: york chiller motor rotation error
Is the chiller equipped with a unit fitted liquid cooled solid state starter or with an external motor starter?
regards,
Entropie
-
13-12-2008, 06:31 AM #7
Re: york chiller motor rotation error
guys problem was solved already....thanks anyways.. current coils inside the motor starter were interchanged thus showing motor phase error in the chiller screen and yes, not transitioning. There were 2 problems. the other one was that the acrel motor protection in the wye-delta starter or in the mains was not configured thus the manual i downloaded was a very big help. because in the acrel site there was no other downloadable manual except for the chinese manual and what a problem it would be to those who are not able to read chinese...like me
-
13-12-2008, 03:43 PM #8
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
Clima Roca York Chiller
By Chinua in forum Air ConditioningReplies: 5Last Post: 13-04-2011, 07:03 PM -
need help on YORK chiller
By nassersh in forum CommercialReplies: 4Last Post: 16-12-2008, 12:47 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM