Re: apac indoor fan motor blowing fuses
Don't know what area the unit is in but start checking the power wiring.
I recently had a system start blowing fuses when the mechanics all checked out OK.
Found bad wiring inside a switched isolator which had corroded due to moisture. Every now and then the moisture would create an electrical short across the phases and blow the fuses.Brian - Newton Abbot, Devon, UK