    daikin G, B series problem



    i have daikin airconditioners serie G ( ft60GV1) and B Series, problem: compressor runing (opereation ) 5 minut then off and run again for 5 minut and off, setting temperature 18 degree celcius and room temperature 27 degree celcius, some body solution ? please write



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: daikin G, B series problem

    You do have it set at cooling and not in dehumidification mode?

    Assuming that you have it set to cooling, try and put it in test mode and see what happens then.

    BTW, when the compressor is running, what is the temperature of the air coming out of the indoor unit?

    I also assume that there are no faultcodes coming up/no lights flashing?

  3. #3
    Join Date
    Aug 2008
    Location
    indonesia
    Posts
    8
    Rep Power
    0

    Re: daikin G, B series problem

    yes, my a/c set at cooling and not in dehumidification mode, compressor runing after power on. and air coming out of the indoor unit is cool, no show fault code, and no flashing led power, thank you

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: daikin G, B series problem

    Quote Originally Posted by yanatahyana View Post
    i have daikin airconditioners serie G ( ft60GV1) and B Series, problem: compressor runing (opereation ) 5 minut then off and run again for 5 minut and off, setting temperature 18 degree celcius and room temperature 27 degree celcius, some body solution ? please write

    What is your placement of indoor unit, do you have any obstacles in front of unit?
    What is room size and shape?
    Do you have clean filters?

  5. #5
    Join Date
    Aug 2008
    Location
    indonesia
    Posts
    8
    Rep Power
    0

    Re: daikin G, B series problem

    no problem for placement of indoor, and indoor dont have any obstacles in front of unit, room size 4 m2, filter clean. my be pcb control error?, or thermistor room problem?, help me

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: daikin G, B series problem

    Quote Originally Posted by yanatahyana View Post
    no problem for placement of indoor, and indoor dont have any obstacles in front of unit, room size 4 m2, filter clean. my be pcb control error?, or thermistor room problem?, help me

    There is your problem! Room size is to small! Or, we could say, that your A/C is way over sized for that room.
    6kW of cooling capacity for 4m^2 room is insanely over sized.

    You need 10 times smaller unit capacity for that room!
    Last edited by nike123; 20-08-2008 at 05:16 AM.

  7. #7
    Join Date
    Aug 2008
    Location
    indonesia
    Posts
    8
    Rep Power
    0

    Re: daikin G, B series problem

    why room temperature 23 "Celsius, whereas temp. set point 18 "celsius

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: daikin G, B series problem

    Quote Originally Posted by yanatahyana View Post
    why room temperature 23 "Celsius, whereas temp. set point 18 "celsius
    Describe your room! Use, height, walls, glass, number of peoples, equipment in room, position of indoor unit.
    But, all that is irrelevant for that size of room and power of A/C!
    That AC cannot work continuously. It works intermittently on "Minmum operating time" and then stops at "Minimum stop time". That room must be highly loaded by sun heat thru lot of glass or something simmilar.

  9. #9
    Join Date
    Aug 2008
    Location
    australia
    Age
    51
    Posts
    46
    Rep Power
    0

    Re: daikin G, B series problem

    dear friend u propebly installed the ontroler neer the indoor unit air out let so the ontrol temperature sanser its picing up out let air temberature not room temp.


    king

  10. #10
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    16
    Rep Power
    0

    Re: daikin G, B series problem

    Quote Originally Posted by a/c.king View Post
    dear friend u propebly installed the ontroler neer the indoor unit air out let so the ontrol temperature sanser its picing up out let air temberature not room temp.


    king
    No...

    Return Air sensor is located within the highwall, please check the resistance of this thermistor
    18 degrees = 27.5 kohms
    20 degrees = 25.1 kohms
    22 degress = 23.0 kohms

    you get the idea

    You need to understand the Daikin controls from this thermistor.

Similar Threads

  1. Leak Testing Daikin K Series VRV
    By jedi in forum Trouble Shooting
    Replies: 8
    Last Post: 21-08-2008, 07:16 PM
  2. Daikin split problem (any ideas)
    By airconjohn in forum Air Conditioning
    Replies: 14
    Last Post: 17-02-2008, 08:40 PM
  3. VRV fault
    By Jase in forum Air Conditioning
    Replies: 10
    Last Post: 16-05-2007, 08:21 PM
  4. Daikin FH series problem
    By pdingle in forum Air Conditioning
    Replies: 7
    Last Post: 13-08-2006, 06:45 PM
  5. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •