19-08-2008, 07:34 AM #1
daikin G, B series problem
i have daikin airconditioners serie G ( ft60GV1) and B Series, problem: compressor runing (opereation ) 5 minut then off and run again for 5 minut and off, setting temperature 18 degree celcius and room temperature 27 degree celcius, some body solution ? please write
-
19-08-2008, 09:16 AM #2
Re: daikin G, B series problem
You do have it set at cooling and not in dehumidification mode?
Assuming that you have it set to cooling, try and put it in test mode and see what happens then.
BTW, when the compressor is running, what is the temperature of the air coming out of the indoor unit?
I also assume that there are no faultcodes coming up/no lights flashing?
-
19-08-2008, 04:06 PM #3
Re: daikin G, B series problem
yes, my a/c set at cooling and not in dehumidification mode, compressor runing after power on. and air coming out of the indoor unit is cool, no show fault code, and no flashing led power, thank you
-
19-08-2008, 04:23 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
20-08-2008, 02:02 AM #5
Re: daikin G, B series problem
no problem for placement of indoor, and indoor dont have any obstacles in front of unit, room size 4 m2, filter clean. my be pcb control error?, or thermistor room problem?, help me
-
20-08-2008, 05:04 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: daikin G, B series problem
Last edited by nike123; 20-08-2008 at 05:16 AM.
-
20-08-2008, 09:28 AM #7
Re: daikin G, B series problem
why room temperature 23 "Celsius, whereas temp. set point 18 "celsius
-
20-08-2008, 09:56 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: daikin G, B series problem
Describe your room! Use, height, walls, glass, number of peoples, equipment in room, position of indoor unit.
But, all that is irrelevant for that size of room and power of A/C!
That AC cannot work continuously. It works intermittently on "Minmum operating time" and then stops at "Minimum stop time". That room must be highly loaded by sun heat thru lot of glass or something simmilar.
-
20-08-2008, 10:15 AM #9
Re: daikin G, B series problem
dear friend u propebly installed the ontroler neer the indoor unit air out let so the ontrol temperature sanser its picing up out let air temberature not room temp.
king
-
22-08-2008, 04:51 AM #10
Re: daikin G, B series problem
Similar Threads
-
Leak Testing Daikin K Series VRV
By jedi in forum Trouble ShootingReplies: 8Last Post: 21-08-2008, 07:16 PM -
Daikin split problem (any ideas)
By airconjohn in forum Air ConditioningReplies: 14Last Post: 17-02-2008, 08:40 PM -
VRV fault
By Jase in forum Air ConditioningReplies: 10Last Post: 16-05-2007, 08:21 PM -
Daikin FH series problem
By pdingle in forum Air ConditioningReplies: 7Last Post: 13-08-2006, 06:45 PM -
Daikin problem
By Jambo in forum Trouble ShootingReplies: 4Last Post: 28-07-2006, 07:42 PM