Help on a Daikin FXYFP32KBV19
Hi, my first post as a new member
Working on a VRV system one of the indoor units when switched off or in fan only mode freezes up, i have replaced the pcb and it still does not work could it possibly be the expansion device? I have checked the output from the board to the expansion valve & have 24 volts on all cables weather the unit is asking for cooling or not.
I'm stuck please help.
-
10-07-2008, 07:42 PM #2
Re: Help on a Daikin FXYFP32KBV19
Is this on a heat recovery system?
-
10-07-2008, 09:12 PM #3
Re: Help on a Daikin FXYFP32KBV19
i would say that the valve is open and not shutting down or the valve is passing. i have had 2 bad valves that i changed under warrenty
hope this helps
kp3
-
11-07-2008, 07:49 AM #4
Re: Help on a Daikin FXYFP32KBV19
Yes it is a heat recovery system, & i'm gonna change the valve.